#76682 - 03/12/01 06:44 PM Electrical Calculations  
AFFELEC  Offline
Junior Member
Joined: Mar 2001
Posts: 5
DEKALB, IL, DEKALB
How do you calculate the service requirements for a hotel with multiple electric heat / a/c units. There are approx. 22 of them. I believe you would take th KW each times number of units with standard amperage formula times 125%, but not sure. These units would be on their own service with nothing else.


2017 / 2014 NEC & Related Books and Study Guides

#76683 - 03/12/01 07:04 PM Re: Electrical Calculations  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,311
220-15 seems to be what your after. Note it says "computed at 100%" , which only means no derating of more than 1 unit to me.


#76684 - 03/12/01 07:26 PM Re: Electrical Calculations  
AFFELEC  Offline
Junior Member
Joined: Mar 2001
Posts: 5
DEKALB, IL, DEKALB
i belive your right thanks . if my math is correct then 5,150 watts x 22 , 208 v ea 2wire , 22 amps ea. , total 110 kw w/ 3 phase factor then i should come up with 305.32 amps so a 400 a service 120/208 3 phase would be more than adequate however we put in 2 main lug panelboards 42 cir (225 a)becuase the 2 pole breakers could only occupy 40 spaces ea panel . might put in a 3rd to lighten load on ea of these.then again the extra capacity might be nice w/ a 600 a service and distribution board



Member Spotlight
Bill Addiss
Bill Addiss
NY, USA
Posts: 3,878
Joined: October 2000
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.012s Queries: 14 (0.002s) Memory: 0.7508 MB (Peak: 0.8738 MB) Zlib enabled. Server Time: 2017-09-22 15:22:51 UTC