i belive your right thanks . if my math is correct then 5,150 watts x 22 , 208 v ea 2wire , 22 amps ea. , total 110 kw w/ 3 phase factor then i should come up with 305.32 amps so a 400 a service 120/208 3 phase would be more than adequate however we put in 2 main lug panelboards 42 cir (225 a)becuase the 2 pole breakers could only occupy 40 spaces ea panel . might put in a 3rd to lighten load on ea of these.then again the extra capacity might be nice w/ a 600 a service and distribution board