#50280 - 03/28/05 07:00 PM do you wire a bar area the same as a kitchen ?  
toddyh  Offline
Junior Member
Joined: Mar 2005
Posts: 3
budd lake,nj
I have been wiring bar areas just as I do kitchens with 2 circuits on the counter top. Do I need to do that? Some one was telling me I do not and I asked the inspector and he never gave me a straight answer. If you have a article number that would be great thank you guys.
Todd


Work Gear for Electricians and the Trades

#50281 - 03/28/05 08:10 PM Re: do you wire a bar area the same as a kitchen ?  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,099
Estero,Fl,usa
If there are no facillities for cooking food I don't believe this is a "kitchen". The only requirement is the GFCI assuming this is a "wet" bar. It could be served from a general lighting circuit IMHO. Certainly nobody will complain about having extra capacity but I doubt 4800va is justified.


Greg Fretwell

#50282 - 03/28/05 08:14 PM Re: do you wire a bar area the same as a kitchen ?  
Celtic  Offline
Member
Joined: Feb 2005
Posts: 361
NJ
A blender, a microwave, a lamp on the bar...who knows what else?
If you put in an outlet, the owner(comm. or home) will find something to plug into it!


~~ CELTIC ~~
...-= NJ =-...

#50283 - 03/28/05 11:42 PM Re: do you wire a bar area the same as a kitchen ?  
PCBelarge  Offline
Member
Joined: Jun 2003
Posts: 681
Dobbs Ferry, NY, USA
The only reference to wet bar sinks is 210.8(A)(7).

I do not know of a reference in the NEC that even requires the wet bar counter to have receptacles, let alone having 2 circuits.


Branch circuits required - 210.11(C)

Receptacles required - 210.52

no mention of wet bars in these sections.


Pierre Belarge

#50284 - 03/29/05 03:39 AM Re: do you wire a bar area the same as a kitchen ?  
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
Of course there should be 2 circuits!

One for each blender - Margarita's and Daquerie's


Mark Heller
"Well - I oughta....." -Jackie Gleason


Member Spotlight
togol
togol
NW In. USA
Posts: 421
Joined: September 2005
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.017s Queries: 14 (0.003s) Memory: 0.7681 MB (Peak: 0.9059 MB) Zlib enabled. Server Time: 2017-07-25 12:41:12 UTC