Boiler Wiring #42701
09/24/04 08:02 PM
09/24/04 08:02 PM
C
CRM  Offline OP
Member
Joined: Feb 2004
Posts: 74
Alberta Canada
At work today, I had to rewire 4 heating system boilers in a commercial building. Three of these boilers had to run off of one thermostat, I was going to use a 3 pole control relay to accomplish this. Each of these boilers has it's own 24volt control circuit, a (R) and a (W) terminal to fire the boiler. The previous installer didn't use a relay, he joined all 3 (R) terminals together and all 3 (W) terminals together, from each boiler and put them on 1 thermostat. My thinking has always been, if you join 3 separate control systems together you would short them out, possibly burning out the transformers, but these boilers have worked like this for about a year. Is it okay to do this without a relay. Thanks for any replies.

Work Gear for Electricians and the Trades
Re: Boiler Wiring #42702
09/24/04 08:55 PM
09/24/04 08:55 PM
T
twh  Offline
Member
Joined: Mar 2004
Posts: 925
Regina, Sask.
Nothing direct, but I talked to an electrician about that, this week. She told me that they must be on the same phase - something about the interconnected wiring between units. Sorry, but I didn't ask more questions. I'm a little slow before 10 cups of coffee.

Re: Boiler Wiring #42703
09/24/04 09:03 PM
09/24/04 09:03 PM
L
leespark  Offline
Member
Joined: Jan 2004
Posts: 54
Massachusetts
It may work but it is not the way to do it IMO. Transformers do weird things when they "talk" to each other like that. It could also burn up the t-stat. I do quite a bit of heating-cooling wiring and always keep a couple of "RIB"s (relay in a box) in the truck. Constantly getting me out of a jam (about $12 each).
http://www.functionaldevices.com/ChartPilot.html

Re: Boiler Wiring #42704
09/24/04 09:48 PM
09/24/04 09:48 PM
T
twh  Offline
Member
Joined: Mar 2004
Posts: 925
Regina, Sask.
leespark, I'll ask when I see her again, but I got the impression that it was manufacturer's specs. I agree with you, and she clearly agreed with us, but the manufacturer wins. It didn't work, then, when changed, it did work.

I'll ask.

Re: Boiler Wiring #42705
09/25/04 01:09 PM
09/25/04 01:09 PM
B
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
 
“Jumpering” three control systems with individual control-power transformers through a single contact is very shortsighted—likely unreliable at very least—worse, unpredictably hazardous for boiler-operational safety.

It could very well be that the boilers are not shutting down by the subject thermoset, but instead being repeatedly cycled by safety-limit controls—which may be a very serious error.




[This message has been edited by Bjarney (edited 09-25-2004).]

Re: Boiler Wiring #42706
09/25/04 01:38 PM
09/25/04 01:38 PM
N
Norstarr  Offline
Member
Joined: Sep 2004
Posts: 86
Wi
I feel they were very fortunate not to have had a problem on the control circuits of those boilers for such a long time. I agree with you regarding installing a three pole relay controlled by the thermostat. It looks more professional and should one boilers control circuit fail it would still allow the other ones to continue instead of dropping all three.
Ron

Re: Boiler Wiring #42707
09/25/04 04:09 PM
09/25/04 04:09 PM
C
cpal  Offline
Member
Joined: May 2004
Posts: 162
Cohasset MA
If I'm following you correctly you are suggesting that the 24V power supplies are interconnected. I have not seen that for some time. What Class power supply are you working with? I would check 725.41 (B) Interconnection of Power Sources. Class 2 or Class 3 power sources shall not have the output connections paralleled or otherwise interconnected unless listed for such interconnection.
In my experience parallel systems are unreliable and subject to failure also as mentioned by previous posts.

Re: Boiler Wiring #42708
10/10/04 10:47 PM
10/10/04 10:47 PM
T
twh  Offline
Member
Joined: Mar 2004
Posts: 925
Regina, Sask.
I did follow up on this. My friend's situation was two furnaces running off one stat. The manufacturer's specs were that they were to be fed from the same phase. Two interconnected furnaces, one stat, and approved that way. Sometimes we just have to be good little soldiers and, like it or not, do what we're told.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Posts: 165
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 15
Potseal 14
Popular Topics(Views)
243,554 Are you busy
180,360 Re: Forum
170,838 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.028s Queries: 14 (0.004s) Memory: 0.9926 MB (Peak: 1.1534 MB) Zlib enabled. Server Time: 2018-01-20 00:49:59 UTC