pulling cables into conduit #31375
11/20/03 03:38 PM
11/20/03 03:38 PM
R
rmiell  Offline OP
Member
Joined: Nov 2000
Posts: 242
La Junta, Co. USA
What is the formula used for figuring the amount of pulling force when pulling cables into underground conduit?

I have multiple runs of 2" and 3", all PVC except the upright portions (at one end only) which is steel (90 degree elbows and risers out of the ground). All other elbows in the pull are PVC. The conduit runs all start at an underground vault, then continue out to, at the most, 2 PVC 90's, then to a steel 90, then up to cabinet. The max length will be 300'.

I want to purchase a small tugger, and rope, for pulling these cable (type TC). Most conduits will have only 2 or 3 multi-conductor cables, but one has 8 cables(seven 4-conductor cables and one 12-conductor cable).

Any recommendations on a brand of puller/tugger to purchase?

Rick Miell

Work Gear for Electricians and the Trades
Re: pulling cables into conduit #31376
11/20/03 07:08 PM
11/20/03 07:08 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,918
Brick, NJ USA
Rick:
When it was time to buy a puller, I went for the Greenlee Super Tugger package. Yes, it's big and a little on the heavy side....but I haven't found anything that it can't pull yet.

Longest was 990' of 4x750 CU, 2-90's and a straight shot between. Piece o'cake.

4x600; 4" EMT 22-90-90-22 and 335' five sets was no sweat either.

Did you look in the "Electrical Advertizer", you may consider a "used" or refurb unit, the $$ is good.

John


John
Re: pulling cables into conduit #31377
11/23/03 08:01 AM
11/23/03 08:01 AM
S
sparky  Online Content
Member
Joined: Oct 2000
Posts: 5,344
I'm honestly short on a formula this morning, no doubt one exists...

one simple factor is friction, which i have learned to minimize via the proper sized mouse, dragged both ways with (say a 300' run) a gallon of 77 spoon fed into each end.....

the kcmil introduced (angle of entry aslo considered) slides thru like s**t through a goose...

[Linked Image]

Re: pulling cables into conduit #31378
11/23/03 10:13 AM
11/23/03 10:13 AM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
The company I work for has Greenlee super tuggers and Ultra tuggers along with motorized wire feeding equipment.

All of it is great stuff but big bucks, if you do not see a regular use of this equipment I would look into renting it on an as needed basis.

You can only do one task with this stuff so you better have a lot of pulling to do.

Also this stuff can damage and destroy the cans, enclosures, raceways and of course personal.

I will make the Norm Abram's statement.
[Linked Image]

"Be sure to read, understand and follow the safety directions that come with the equipment". [Linked Image]

Get the right ropes, no stretchy stuff.

On the good side, this stuff works great with lube you will get the wires in.

I have installed four 600 kcmils in 3" EMT 350' through three 90s.

The puller was hitting 7000 lbs at times.



[This message has been edited by iwire (edited 11-23-2003).]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: pulling cables into conduit #31379
11/23/03 12:14 PM
11/23/03 12:14 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Rick,
There is an online pulling calculator here . Note that the limiting factor is often the sidewall pressure (crushing force) at the bend in the conduit run and not the pulling tension itself.
Don


Don(resqcapt19)
Re: pulling cables into conduit #31380
11/27/03 01:34 AM
11/27/03 01:34 AM
K
kinetic  Offline
Member
Joined: Apr 2002
Posts: 156
Phoenix, Arizona
Might be a little small for you but this one interested me for a bit.....well until I saw the price tag. Still looks tempting from time to time. http://www.maxistools.com/product/pullit3000.php


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
waymag
waymag
dallas, texas, USA
Posts: 67
Joined: January 2002
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 16
Potseal 15
Popular Topics(Views)
243,576 Are you busy
180,374 Re: Forum
170,852 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.013s Queries: 14 (0.003s) Memory: 0.9770 MB (Peak: 1.1227 MB) Zlib enabled. Server Time: 2018-01-21 14:43:25 UTC