#30015 - 09/29/03 12:26 AM UF in pipe  
aldav53  Offline
Member
Joined: Aug 2001
Posts: 545
Chandler, AZ USA
I saw a job where the customer ran UF in PVC pipe underground. Now I know your not supposed to run NM but what about UF? Is it legal? I would think it would be.


The Golden Rule - "The man with the gold makes the rule"

Work Gear for Electricians and the Trades

#30016 - 09/29/03 01:41 AM Re: UF in pipe  
stamcon  Offline
Member
Joined: Mar 2001
Posts: 329
So San Francisco CA
The 99NEC permits UF and NM cables to be run in pipe(NM can't be in a "wet" location). 300-5(c) requires cables installed under buildings to be in a raceway. 300-5(d) requires direct buried conductors and cables emerging from the ground to be in an enclosure or raceway from the minimum cover distance to at least 8' above finished grade.


#30017 - 09/30/03 08:31 PM Re: UF in pipe  
Speedy Petey  Offline
Member
Joined: Aug 2003
Posts: 173
Upstate, NY
What about an assembly being in a raceway?
In this case UF and NM are basically the same thing, no?
A sleeve up the side of a structure I can see but not a complete conduit.


Speedy Petey

"Anyone who has never made a mistake has never tried anything new." -Albert Einstein

#30018 - 10/01/03 04:40 AM Re: UF in pipe  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Using PVC to protect NM cable from physical damage is spelled out in 334.15(B)

And 340.10(4) tells us that the rules of 334 will apply to UF cable.

Also 300.5(D)(1) requires direct buried cables and conductors emerging from grade are to be protected from damage.


Bob Badger
Construction & Maintenance Electrician
Massachusetts


Member Spotlight
Bill Addiss
Bill Addiss
NY, USA
Posts: 3,878
Joined: October 2000