UF in pipe #30015 09/28/03 11:26 PM
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
I saw a job where the customer ran UF in PVC pipe underground. Now I know your not supposed to run NM but what about UF? Is it legal? I would think it would be.


The Golden Rule - "The man with the gold makes the rule"
Work Gear for Electricians and the Trades
Re: UF in pipe #30016 09/29/03 12:41 AM
Joined: Mar 2001
Posts: 333
S
stamcon Offline
Member
The 99NEC permits UF and NM cables to be run in pipe(NM can't be in a "wet" location). 300-5(c) requires cables installed under buildings to be in a raceway. 300-5(d) requires direct buried conductors and cables emerging from the ground to be in an enclosure or raceway from the minimum cover distance to at least 8' above finished grade.


Steve
Re: UF in pipe #30017 09/30/03 07:31 PM
Joined: Aug 2003
Posts: 173
S
Speedy Petey Offline
Member
What about an assembly being in a raceway?
In this case UF and NM are basically the same thing, no?
A sleeve up the side of a structure I can see but not a complete conduit.


Speedy Petey

"Anyone who has never made a mistake has never tried anything new." -Albert Einstein
Re: UF in pipe #30018 10/01/03 03:40 AM
Joined: Jan 2003
Posts: 4,391
I
iwire Offline
Moderator
Using PVC to protect NM cable from physical damage is spelled out in 334.15(B)

And 340.10(4) tells us that the rules of 334 will apply to UF cable.

Also 300.5(D)(1) requires direct buried cables and conductors emerging from grade are to be protected from damage.


Bob Badger
Construction & Maintenance Electrician
Massachusetts

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HotLine1
HotLine1
Brick, NJ USA
Posts: 7,218
Joined: April 2002
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 17
Popular Topics(Views)
272,155 Are you busy
206,034 Re: Forum
194,056 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3