I saw a job where the customer ran UF in PVC pipe underground. Now I know your not supposed to run NM but what about UF? Is it legal? I would think it would be.
The Golden Rule - "The man with the gold makes the rule"
The 99NEC permits UF and NM cables to be run in pipe(NM can't be in a "wet" location). 300-5(c) requires cables installed under buildings to be in a raceway. 300-5(d) requires direct buried conductors and cables emerging from the ground to be in an enclosure or raceway from the minimum cover distance to at least 8' above finished grade.
What about an assembly being in a raceway? In this case UF and NM are basically the same thing, no? A sleeve up the side of a structure I can see but not a complete conduit.
Speedy Petey