NM in conduit : interior installation #22100
02/18/03 12:58 PM
02/18/03 12:58 PM
I
ikauffma  Offline OP
Member
Joined: Feb 2003
Posts: 10
Waynesboro, PA USA
Hello All!

Hope everybody in the mid/north east got dug out o.k.

I am going to add an outlet to an existing circuit in my garage. To get the run down the wall, I would like to use 1/2" electrical type PVC and same type of box. I am using a GFCI recpt. on #12/2 NM. I've read some posts on NM in conduit in outside situations, but haven't found any info for interior stuff. Anybody know of anything in the NEC on this?

Thanks much for your info!

Ian

Work Gear for Electricians and the Trades
Re: NM in conduit : interior installation #22101
02/18/03 01:34 PM
02/18/03 01:34 PM
D
dana1028  Offline
Member
Joined: Jan 2002
Posts: 163
San Carlos, CA
334.15(B) - "The cable (NM) shall be protected from physical damage where necessary by conduit..." this section does not differentiate indoors/outdoors.

RE: 1/2" conduit
See Cahp. 9 Tables - Notes to Tables - #9
"A multiconductor cable ....shall be treated as a single conductor for calculating percentage fill area...."

I've never done the arithmetic but if I remember correctly from a previous post NM would require 3/4" conduit to be in compliance.

Re: NM in conduit : interior installation #22102
02/18/03 08:19 PM
02/18/03 08:19 PM
E
Elzappr  Offline
Member
Joined: Dec 2001
Posts: 270
Oregon
I've always added a set of fittings at the end of the conduit so that a 2-screw romex connector could clamp the cable where it enters the conduit. I strip away the cable sheath (for the part of the cable that is going to be in the conduit) up to where the fittings are, so that only the conductors are in the conduit, avoiding problems about conduit fill. This is equivalent to entering a box. I just consider the conduit as a long skinny extension of the box. I never heard of anyone challenging this set-up. I certainly don't see any hazard in doing it this way.

[This message has been edited by Elzappr (edited 02-18-2003).]

Re: NM in conduit : interior installation #22103
02/20/03 03:46 PM
02/20/03 03:46 PM
I
ikauffma  Offline OP
Member
Joined: Feb 2003
Posts: 10
Waynesboro, PA USA
dana1028 and Elzappr;

Thanks for the info! I appreciate your help!

Ian


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Scott35
Scott35
Anaheim, CA. USA
Posts: 2,708
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 15
Popular Topics(Views)
243,606 Are you busy
180,422 Re: Forum
170,875 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.011s Queries: 14 (0.002s) Memory: 0.9578 MB (Peak: 1.0914 MB) Zlib enabled. Server Time: 2018-01-24 07:47:41 UTC