ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Trumpy 3
Recent Posts
Feed to spa panel
by HotLine1. 06/25/17 05:28 PM
Weatherhead, POA, height?
by HotLine1. 06/24/17 02:37 PM
Windows 7 update problem
by ampherder. 06/21/17 07:01 AM
Norwegian power?
by dsk. 06/19/17 03:40 PM
Anyone ever take a Furnas A14D drum sw apart?
by gfretwell. 06/17/17 08:14 PM
New in the Gallery:
SE cable question
Popular Topics(Views)
238,222 Are you busy
173,438 Re: Forum
166,245 Need opinion
Who's Online Now
0 registered members (), 41 guests, and 9 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#214139 - 10/12/14 10:30 PM Daisy chaining on 2pole 30 amp breaker??  
JoeJoeB  Offline
New Member
Joined: Oct 2014
Posts: 4
Boston, MA
Hello, I'd like some input from licensed electricians in MA please.
I'm a home inspector and I have a builder who wants to install 2 4-wire 30amp outlets on a single 30amp double-pole breaker in a detached garage workshop (arc weld,etc.). Not being a licensed electrician, I can't site the actual code on this one, but my gut is that it's better off being 2 separate circuits. The owner claims that due to his needs he would never be running both at same time. I say, what about the next guy who buys the house who has different plans?
Are these outlets even really engineered to be daisy chained?
Also, even if they were pig-tailed in a separate j-box, the argument that they're protected against overload by the breaker tripping seems weak. I see a tripping breaker as a last line of defense against fire, not something I really want to rely on if I can help it. I've seen so many corroded breakers that don't trip when needed.
What do you guys think? Is there an actual code that says you can or cannot do? Or is this up to the local electrical inspector.
Thx- Joe


Work Gear for Electricians and the Trades

#214140 - 10/12/14 11:54 PM Re: Daisy chaining on 2pole 30 amp breaker?? [Re: JoeJoeB]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,085
Estero,Fl,usa
Are they feeding 2 receptacles? If so, you are not going to find anything.


Greg Fretwell

#214141 - 10/13/14 01:26 AM Re: Daisy chaining on 2pole 30 amp breaker?? [Re: JoeJoeB]  
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
He's good to go -- as long as he's using 30A outlets.





Tesla

#214143 - 10/13/14 12:50 PM Re: Daisy chaining on 2pole 30 amp breaker?? [Re: JoeJoeB]  
ghost307  Offline
Member
Joined: May 2005
Posts: 902
Chicago Illinois USA
Absolutely not a problem as long as he uses 10 AWG wire (or larger).

There's no difference between this and allowing more than a single 15A receptacle on a 15A breaker.

If the next guy tries to use both at the same time the breaker will protect things; the same way that the 15A breaker would react to someone running his PC, printer, router, TV, videogame, Xmas tree lights and a bunch of chargers off of a single receptacle in the living room.


Ghost307

#214144 - 10/13/14 03:15 PM Re: Daisy chaining on 2pole 30 amp breaker?? [Re: JoeJoeB]  
JoeJoeB  Offline
New Member
Joined: Oct 2014
Posts: 4
Boston, MA
Appreciate the feedback!


#214145 - 10/13/14 03:22 PM Re: Daisy chaining on 2pole 30 amp breaker?? [Re: JoeJoeB]  
electure  Offline


Member
Joined: Dec 2000
Posts: 4,259
Fullerton, CA USA
It all depends which Code it's under.

It's OK by the NEC.

The IRC however, prohibits multiple receptacles on circuits over 20 Amps


#214146 - 10/13/14 09:30 PM Re: Daisy chaining on 2pole 30 amp breaker?? [Re: JoeJoeB]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,085
Estero,Fl,usa
Interesting Scott.
Florida did not pick up the IRC electrical articles, simply adopting the NEC, pretty much unaltered. There are only a couple of changes. (adding bonding metal studs and removing the GFCI requirement on some hardwired pool pumps).


#214148 - 10/14/14 02:22 PM Re: Daisy chaining on 2pole 30 amp breaker?? [Re: ghost307]  
Texas_Ranger  Offline
Member
Joined: Dec 2001
Posts: 2,397
Vienna, Austria
Originally Posted by ghost307
Absolutely not a problem as long as he uses 10 AWG wire (or larger).

There's no difference between this and allowing more than a single 15A receptacle on a 15A breaker.

If the next guy tries to use both at the same time the breaker will protect things; the same way that the 15A breaker would react to someone running his PC, printer, router, TV, videogame, Xmas tree lights and a bunch of chargers off of a single receptacle in the living room.

Make that a laser printer and add a coffee pot or space heater and you're getting there. All the other gadgets are in the lower double-digit watt range and awfully unlikely to trip a breaker.



Member Spotlight
togol
togol
NW In. USA
Posts: 421
Joined: September 2005
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.014s Queries: 15 (0.003s) Memory: 0.7941 MB (Peak: 0.9563 MB) Zlib enabled. Server Time: 2017-06-26 03:43:17 UTC