ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Recent Posts
VFD MotorFeeders
by gfretwell. 10/17/17 10:01 PM
What do you do?
by gfretwell. 10/17/17 01:08 AM
Good ol' copper pipe in the fuse holder trick
by HotLine1. 10/16/17 07:16 PM
Generator Cable Sizing
by HotLine1. 10/16/17 07:13 PM
Another generator question
by HotLine1. 10/16/17 07:02 PM
New in the Gallery:
Gallery Test
Popular Topics(Views)
241,350 Are you busy
177,303 Re: Forum
168,928 Need opinion
Who's Online Now
0 registered members (), 52 guests, and 12 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
Page 1 of 3 1 2 3
#205629 - 03/15/12 01:07 AM 100 W HPS fixture issue  
Merlin  Offline
Member
Joined: Jan 2004
Posts: 170
NW Indiana
I have a customer with a 100W HPS fixture on an outbuilding. The fixture is photoeye controlled. Almost everytime that a large load starts in the house (A/C, sewage ejector pump, ect.), the light shuts off and eventually comes back on.

The outbuilding and house are both on seperate loadcenters and feed from the same main panel at the meter. It appears to me that this is caused by voltage drop. Correct?? I even switch the fixture circuit to the opposite phase and it still does it. Could this be simply a photoeye problem, or utility service voltage drop???? Any suggestions?


Work Gear for Electricians and the Trades

#205630 - 03/15/12 04:02 AM Re: 100 W HPS fixture issue [Re: Merlin]  
sparkyinak  Offline
Member
Joined: Jul 2007
Posts: 1,327
Alaska
Possibly the transformer is over loaded by other services. What's the incoming voltage at night? It tends to be a little lower in the evenings then the day


"Live Awesome!" - Kevin Carosa

#205632 - 03/15/12 09:34 AM Re: 100 W HPS fixture issue [Re: sparkyinak]  
wire_twister  Offline
Member
Joined: Jul 2007
Posts: 265
Georgia USA
+1 with sparky, check the voltage in the evening, and look at the size of the transformer, and its load. Call the POCO and ask for someone to come out and look.


Jimmy

Life is tough, Life is tougher when you are stupid

#205633 - 03/15/12 09:58 AM Re: 100 W HPS fixture issue [Re: Merlin]  
Merlin  Offline
Member
Joined: Jan 2004
Posts: 170
NW Indiana
This is in a rural area, only service on this transformer. voltage. Under start-up surge from A/C or sewage pump, I saw it drop to 112 for about 1/2 second. I switched the fixture to the "higher" phase (121) and it still dropped out under surge.


#205634 - 03/15/12 10:33 AM Re: 100 W HPS fixture issue [Re: Merlin]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,872
Brick, NJ USA
Merlin:
Did you ck the voltage at the fixture, or the source panel?

Sure sounds like a Vd issue...at the fixture.


John

#205635 - 03/15/12 10:37 AM Re: 100 W HPS fixture issue [Re: Merlin]  
jdevlin  Offline
Member
Joined: Aug 2002
Posts: 402
welland ontario canada
One side higher than the other would indicate possible loose neutral issue.


#205636 - 03/15/12 12:21 PM Re: 100 W HPS fixture issue [Re: Merlin]  
twh  Offline
Member
Joined: Mar 2004
Posts: 919
Regina, Sask.
It's probably voltage drop, but try a new bulb to eliminate that before you spend a lot of money on it.


#205637 - 03/15/12 12:51 PM Re: 100 W HPS fixture issue [Re: jdevlin]  
sparkyinak  Offline
Member
Joined: Jul 2007
Posts: 1,327
Alaska
Originally Posted by jdevlin
One side higher than the other would indicate possible loose neutral issue.


I agree with jdelvin that it could be a loose neutral. When A heavy load start on this service, does any lights on the premises get brighter?


"Live Awesome!" - Kevin Carosa

#205639 - 03/15/12 08:24 PM Re: 100 W HPS fixture issue [Re: Merlin]  
wire_twister  Offline
Member
Joined: Jul 2007
Posts: 265
Georgia USA
I agree with the possible loose neutral situation also. As far as the transformer, My house is the only load on a 15 KVA pole pig, it is about 60 feet from the pole to my meter, every time my 4.5 ton AC compressor starts there is a noticible flicker in the lights. Put this same load on a 10 KVA pot and it could pull down enough to turn the light out. What kind of meter did you use to measure the voltage when AC started? Most DVOMs are not fast enough to catch the dip, so it is likely the reading you got was on its way back up before your meter settled down. Just my 2 cents.


Jimmy

Life is tough, Life is tougher when you are stupid

#205640 - 03/15/12 10:32 PM Re: 100 W HPS fixture issue [Re: Merlin]  
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
Rewire your High Pressure Sodium fixture across 230 VAC instead of 120 VAC.

I'm presuming it has a CWA ( Constant Wattage Autoformer ) with multiple taps.

I also suspect that the wire gauge used to feed it needs 240 VAC.

You've made no mention of the distance to the outbuilding.

Check if the photo-eye can be replaced with a 230 VAC sensor, too.

Every time its voltage pulls low it changes its logical state -- which is the primary cause for the HPS to cut out.





Tesla

Page 1 of 3 1 2 3

Member Spotlight
Vlado
Vlado
Croatia
Posts: 28
Joined: February 2011
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 16 (0.003s) Memory: 0.8190 MB (Peak: 0.9986 MB) Zlib enabled. Server Time: 2017-10-18 03:38:49 UTC