AFCI's #19450
12/28/02 03:38 PM
12/28/02 03:38 PM
R
rowdyrudy  Offline OP
Member
Joined: Nov 2002
Posts: 169
Mascoutah, IL USA
In attempting to get as much info as possible for presentation to the full group for discussion, I have found some disturbing items. If anything has changed from the below I'd like to know.
1. AFCI's not compatible with GFCI protected circuits.
2. Combination AFCI/GFCI CB's may be available in the future.
3. No testing device available for AFCI CB's.
4. Disconnect all AFCI's prior to hy-potting a panel.
Several other concerns/shortcomings.
The other panel members are leaning towards rejecting the requirement for AFCI's, as have many jurisdictions. What is the concensus from those who are forced to deal with items like this that are injected into the system prior to having full testing and evaluation. The one that is most disturbing to me is #1. It appears that the mfgrs once again used their influence to get an item in the code before it's time. It makes it real difficult for those who are trying to get legislation passed to accept the NEC.
Rowdy

Work Gear for Electricians and the Trades
Re: AFCI's #19451
12/28/02 04:27 PM
12/28/02 04:27 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
I suggest that you do a search on this forum for AFCI. There are a large number of threads with extensive posts on this subject.
don


Don(resqcapt19)
Re: AFCI's #19452
12/28/02 05:02 PM
12/28/02 05:02 PM
R
rowdyrudy  Offline OP
Member
Joined: Nov 2002
Posts: 169
Mascoutah, IL USA
I have searched the mfgrs and UL sites. That's where I got the info.
Rowdy

Re: AFCI's #19453
12/28/02 06:37 PM
12/28/02 06:37 PM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,344
2nd Don's reply

quickly:

1. AFCI's not compatible with GFCI protected circuits.

no prob, to my knowledge.....

2. Combination AFCI/GFCI CB's may be available in the future.

as i understand it, yes.....


3. No testing device available for AFCI CB's.

no,there was a thread here, and new 'tester'.

4. Disconnect all AFCI's prior to hy-potting a panel.

true, i believe it is stated on the packaging.

Re: AFCI's #19454
12/29/02 03:53 AM
12/29/02 03:53 AM
N
nesparky  Offline
Member
Joined: Jun 2001
Posts: 642
omaha,ne
Because of the lack of reliable accurate historical information and a lot of manufacturers hype, many jurisdictions declined to be part of the beta test of these devices.
as for your questions
# 1 no need to put a gfi and afci on same circuit.
#2 Cutler hammer and square D afci have gfi circuitry in thier afci. So thier rep's claim as does thier brocures. It set somewhere from 30 to 70 mA according to the rep's depending on manufacturer.
#3 true only device marketed is a waste of maney it has a problem according to a recall notice I saw
#4 Any device with sensitive electronics will not stand a hipot test including gfi breakers.
As don said AFCI's have been the subject of a lot of posts here. I for one still do not believe the are worth the cost.


ed
Re: AFCI's #19455
12/29/02 10:49 AM
12/29/02 10:49 AM
sparky66wv  Offline
Member
Joined: Nov 2000
Posts: 2,236
West Virginia
Allow me to add:
The AFCIs, for the most part, are Class B GFCIs. They cannot be used as Class A GFCI protection.


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Re: AFCI's #19456
12/29/02 12:17 PM
12/29/02 12:17 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
We should not be calling the ground fault protection that is built into the AFCI breaker GFCI. It is not GFCI, with the exception of the dual listed CH product, it is GFP. As sparky66 pointed out, the GFP in the AFCI device is set to operate much above the required setpoint of a GFCI device. The term GFCI should be reserved for use for ground fault protection devices that are intended to protect people. The term GFP should be used for all other ground fault protection devices. When you get down to studying the details of the AFCI breaker operation, you will find that in many cases the actual protection is provided by the GFP circuit and not the fancy arc detection circuit.
don


Don(resqcapt19)
Re: AFCI's #19457
12/29/02 02:19 PM
12/29/02 02:19 PM
E
ElectricAL  Offline
Member
Joined: Oct 2001
Posts: 597
Minneapolis, MN USA
NESparky,

I can think of at least one scenario that leads to a required GFI on an AFCI protected circuit.

If I elect to put an exterior outlet on the deck (hypothetical deck) outside the bedroom, when the deck access is through the bedroom, I'll find it awful tempting to tag on the deck outlet and light to the bedroom circuit, especially if the job is competitively bid.

Admittedly, not all deck situations will require a GFI for the outlet on the deck, but many will.

Exploring the possibilities,

Al


Al Hildenbrand
Re: AFCI's #19458
12/30/02 01:47 AM
12/30/02 01:47 AM
N
nesparky  Offline
Member
Joined: Jun 2001
Posts: 642
omaha,ne
Good point AL
Since my home state deleted the AFCI requirements when the 2002 code was adopted, I do not have to worry about that problem.


ed

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
mxslick
mxslick
Atomic City, ID USA
Posts: 803
Joined: October 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 15
Potseal 15
Popular Topics(Views)
243,597 Are you busy
180,400 Re: Forum
170,867 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.019s Queries: 14 (0.005s) Memory: 1.0003 MB (Peak: 1.1669 MB) Zlib enabled. Server Time: 2018-01-23 05:47:42 UTC