ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Potseal 10
Admin 5
Recent Posts
Old decora style outlets
by Lostazhell. 04/22/17 07:59 PM
Dimmable LED 2x4 lay in fixtures
by gfretwell. 04/22/17 01:14 PM
Permit Snafus...AHJs and Contractors Jump in
by gfretwell. 04/22/17 01:11 PM
How do you find a good employee?
by HotLine1. 04/22/17 10:44 AM
Electrode boilers question
by SteveFehr. 04/21/17 08:32 AM
New in the Gallery:
SE cable question
Popular Topics(Views)
234,477 Are you busy
169,092 Re: Forum
162,478 Need opinion
Who's Online Now
0 registered members (), 41 guests, and 7 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
Page 1 of 2 1 2
#192692 - 02/25/10 05:18 PM Neutrals Combined in Outlet Box Question  
rwilsond  Offline
New Member
Joined: Aug 2005
Posts: 5
Rancho Santa Margarita, CA
Here's an oddity I came across. An electrician was called to a house, because of lights flickering. He came to believe there was an open in the neutral of a 2-wire branch circuit. But he was unable to locate and correct the open. So, he jumpered the neutral to the neutral of another 2-wire branch circuit, in an existing outlet box.

Which sections of the NEC did he violate?



2017 / 2014 NEC & Related Books and Study Guides

#192693 - 02/25/10 06:12 PM Re: Neutrals Combined in Outlet Box Question [Re: rwilsond]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,069
Estero,Fl,usa
300.3(B)? 310.4?


Greg Fretwell

#192695 - 02/25/10 07:37 PM Re: Neutrals Combined in Outlet Box Question [Re: gfretwell]  
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 822
Michigan
I'd agree with you 300.3(B).


#192703 - 02/26/10 11:19 AM Re: Neutrals Combined in Outlet Box Question [Re: Yoopersup]  
Rewire  Offline
Member
Joined: Feb 2008
Posts: 165
Missouri
210.4 (B)


#192704 - 02/26/10 11:51 AM Re: Neutrals Combined in Outlet Box Question [Re: Rewire]  
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 822
Michigan
210.4(B) is for ungrounded conductors not grounded conductors.


#192718 - 02/26/10 09:33 PM Re: Neutrals Combined in Outlet Box Question [Re: Yoopersup]  
Rewire  Offline
Member
Joined: Feb 2008
Posts: 165
Missouri
Originally Posted by Yoopersup
210.4(B) is for ungrounded conductors not grounded conductors.
The OP said he was dealing with 2 MWBC so these 4 wires now comprise the MWBC so all 4 breakers would need to disconnect at the same time its a subtle violation.


#192719 - 02/26/10 10:33 PM Re: Neutrals Combined in Outlet Box Question [Re: Rewire]  
wa2ise  Offline
Member
Joined: Nov 2002
Posts: 782
Oradell NJ USA
I don't know the code, especially chapter and verse, but I think you'd have 4 bad results: a) depending on the phasing of the other circuit, if it happens to be the same phase you could get an overloaded neutral, b) Violation of that code rule saying "no paralleled wires (except for a few well restricted exceptions)", and c)the other circuit's breaker needs to be ganged with the first circuit's breaker. And you'd have current passing thru the hot wire of one cable (raceway) and returning thru a separate cable (raceway) neutral wire (because of an open on the first raceway's neutral) which I'm sure is a 4th violation and if not, still undesirable. You'd have a large loop of 60Hz magnetic activity happening, and in severe enough cases you could get magnetic inductive heating of connector and box hardware.


#192720 - 02/27/10 12:31 AM Re: Neutrals Combined in Outlet Box Question [Re: wa2ise]  
Rewire  Offline
Member
Joined: Feb 2008
Posts: 165
Missouri
300.3 B(4) allows seperate cables as long as you comply with 300.20 B


#192742 - 02/28/10 08:53 PM Re: Neutrals Combined in Outlet Box Question [Re: Rewire]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,808
Brick, NJ USA
Rewire:

Originally Posted by Rewire
Originally Posted by Yoopersup
210.4(B) is for ungrounded conductors not grounded conductors.
The OP said he was dealing with 2 MWBC so these 4 wires now comprise the MWBC so all 4 breakers would need to disconnect at the same time its a subtle violation.


I think you should go back to the OP again! Two (2) wire branch circuits IMHO are a hot & a neutral. Therefore he now has two hots (of unknown phase) and one neutral.

Yes, a 2 pole CB (single handle) would be required, and yes, the neutral could be overloaded depending on the phasing, but that is unknown as of now.

It's a dangerous practice to do what the OP found.


John

#192744 - 02/28/10 10:02 PM Re: Neutrals Combined in Outlet Box Question [Re: HotLine1]  
Rewire  Offline
Member
Joined: Feb 2008
Posts: 165
Missouri
Originally Posted by HotLine1
Rewire:

Originally Posted by Rewire
Originally Posted by Yoopersup
210.4(B) is for ungrounded conductors not grounded conductors.
The OP said he was dealing with 2 MWBC so these 4 wires now comprise the MWBC so all 4 breakers would need to disconnect at the same time its a subtle violation.


I think you should go back to the OP again! Two (2) wire branch circuits IMHO are a hot & a neutral. Therefore he now has two hots (of unknown phase) and one neutral.

Yes, a 2 pole CB (single handle) would be required, and yes, the neutral could be overloaded depending on the phasing, but that is unknown as of now.

It's a dangerous practice to do what the OP found.
The OP needs clarity, a branch circuit by definition has 2 conductors so stating it was a 2 wire branch circuit was a bit misleading I made the assumption he was speaking of a MWBC either way a handle tie breaker would be required a simple voltage check at the box would tell you if you were on the same phase.


Page 1 of 2 1 2

Member Spotlight
sbi
sbi
indiana
Posts: 47
Joined: March 2008
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 16 (0.002s) Memory: 0.8185 MB (Peak: 1.0012 MB) Zlib enabled. Server Time: 2017-04-23 05:31:37 UTC