Neutrals Combined in Outlet Box Question #192692 02/25/10 04:18 PM
Joined: Aug 2005
Posts: 5
R
rwilsond Offline OP
New Member
Here's an oddity I came across. An electrician was called to a house, because of lights flickering. He came to believe there was an open in the neutral of a 2-wire branch circuit. But he was unable to locate and correct the open. So, he jumpered the neutral to the neutral of another 2-wire branch circuit, in an existing outlet box.

Which sections of the NEC did he violate?


2017 / 2014 NEC & Related Books and Study Guides
Re: Neutrals Combined in Outlet Box Question [Re: rwilsond] #192693 02/25/10 05:12 PM
Joined: Jul 2004
Posts: 9,571
G
gfretwell Online Content
Member
300.3(B)? 310.4?


Greg Fretwell
Re: Neutrals Combined in Outlet Box Question [Re: gfretwell] #192695 02/25/10 06:37 PM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline
Member
I'd agree with you 300.3(B).

Re: Neutrals Combined in Outlet Box Question [Re: Yoopersup] #192703 02/26/10 10:19 AM
Joined: Feb 2008
Posts: 165
R
Rewire Offline
Member
210.4 (B)

Re: Neutrals Combined in Outlet Box Question [Re: Rewire] #192704 02/26/10 10:51 AM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline
Member
210.4(B) is for ungrounded conductors not grounded conductors.

Re: Neutrals Combined in Outlet Box Question [Re: Yoopersup] #192718 02/26/10 08:33 PM
Joined: Feb 2008
Posts: 165
R
Rewire Offline
Member
Originally Posted by Yoopersup
210.4(B) is for ungrounded conductors not grounded conductors.
The OP said he was dealing with 2 MWBC so these 4 wires now comprise the MWBC so all 4 breakers would need to disconnect at the same time its a subtle violation.

Re: Neutrals Combined in Outlet Box Question [Re: Rewire] #192719 02/26/10 09:33 PM
Joined: Nov 2002
Posts: 790
W
wa2ise Offline
Member
I don't know the code, especially chapter and verse, but I think you'd have 4 bad results: a) depending on the phasing of the other circuit, if it happens to be the same phase you could get an overloaded neutral, b) Violation of that code rule saying "no paralleled wires (except for a few well restricted exceptions)", and c)the other circuit's breaker needs to be ganged with the first circuit's breaker. And you'd have current passing thru the hot wire of one cable (raceway) and returning thru a separate cable (raceway) neutral wire (because of an open on the first raceway's neutral) which I'm sure is a 4th violation and if not, still undesirable. You'd have a large loop of 60Hz magnetic activity happening, and in severe enough cases you could get magnetic inductive heating of connector and box hardware.

Re: Neutrals Combined in Outlet Box Question [Re: wa2ise] #192720 02/26/10 11:31 PM
Joined: Feb 2008
Posts: 165
R
Rewire Offline
Member
300.3 B(4) allows seperate cables as long as you comply with 300.20 B

Re: Neutrals Combined in Outlet Box Question [Re: Rewire] #192742 02/28/10 07:53 PM
Joined: Apr 2002
Posts: 7,235
HotLine1 Offline
Member
Rewire:

Originally Posted by Rewire
Originally Posted by Yoopersup
210.4(B) is for ungrounded conductors not grounded conductors.
The OP said he was dealing with 2 MWBC so these 4 wires now comprise the MWBC so all 4 breakers would need to disconnect at the same time its a subtle violation.


I think you should go back to the OP again! Two (2) wire branch circuits IMHO are a hot & a neutral. Therefore he now has two hots (of unknown phase) and one neutral.

Yes, a 2 pole CB (single handle) would be required, and yes, the neutral could be overloaded depending on the phasing, but that is unknown as of now.

It's a dangerous practice to do what the OP found.


John
Re: Neutrals Combined in Outlet Box Question [Re: HotLine1] #192744 02/28/10 09:02 PM
Joined: Feb 2008
Posts: 165
R
Rewire Offline
Member
Originally Posted by HotLine1
Rewire:

Originally Posted by Rewire
Originally Posted by Yoopersup
210.4(B) is for ungrounded conductors not grounded conductors.
The OP said he was dealing with 2 MWBC so these 4 wires now comprise the MWBC so all 4 breakers would need to disconnect at the same time its a subtle violation.


I think you should go back to the OP again! Two (2) wire branch circuits IMHO are a hot & a neutral. Therefore he now has two hots (of unknown phase) and one neutral.

Yes, a 2 pole CB (single handle) would be required, and yes, the neutral could be overloaded depending on the phasing, but that is unknown as of now.

It's a dangerous practice to do what the OP found.
The OP needs clarity, a branch circuit by definition has 2 conductors so stating it was a 2 wire branch circuit was a bit misleading I made the assumption he was speaking of a MWBC either way a handle tie breaker would be required a simple voltage check at the box would tell you if you were on the same phase.

Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
pcsailor
pcsailor
Minneapolis, MN, USA
Posts: 21
Joined: September 2019
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,704 Are you busy
209,627 Re: Forum
196,966 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3