#18837 - 12/15/02 01:43 PM Question About Receptacles  
ThinkGood  Offline
Member
Joined: Aug 2002
Posts: 1,081
Milwaukee, WI
Hi, all. I've been hanging around here for a few months, learning, trying to contribute, and now I have some questions.

One is as follows.

A GFCI receptacle, such as this one
[Linked Image]
is listed as a 15 amp receptacle, 20 amps feed-through.

I take this to mean that receptacles that are attached to the LOAD side of the GFCI (that is, those receptacles that would be after the GFCI, so if the GFCI trips, those receptacles would also loose power) can be 20 amp receptacles.

If this is the case, why wouldn't the GFCI receptacle be rated at 20 amps, appearing as such [Linked Image]

I am having trouble comprehending how a device rated at 15 amps can be on a circuit with a 20 amp breaker. Does that not present a hazard of the receptacle overheating? (Not just in this example of GFCI, but on a circuit that would have a 20 amp breaker, 12 AWG cable, but receptacles rated for 15 amps. Doesn't that allow for overheating of the receptacle and/or that which is powered by it?)

I look forward to your informative answers.

Thanks.

[This message has been edited by ThinkGood (edited 12-15-2002).]

[This message has been edited by ThinkGood (edited 12-15-2002).]


Work Gear for Electricians and the Trades

#18838 - 12/15/02 02:57 PM Re: Question About Receptacles  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,311
ThinkGood,

actually i believe our Canadian friends here would agree with you, we in the US just depend on 'diversity' a tad more...

~S


#18839 - 12/15/02 03:14 PM Re: Question About Receptacles  
electric-ed  Offline
Member
Joined: Jul 2002
Posts: 175
Canada
ThinkGood,

Hey, I notice that you install your receptacles U-ground up. [Linked Image]

I'm with you, man.

Ed


#18840 - 12/15/02 07:03 PM Re: Question About Receptacles  
classicsat  Offline
Member
Joined: Nov 2002
Posts: 456
FWIW, the moulding of a spent GFCI recepticle
I dissected, had the t-slot so with minor
modification to the mould could make it a 20A, howver I don't think the contacts could
accept a horizontal prong.


#18841 - 12/15/02 07:37 PM Re: Question About Receptacles  
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
Thinkgood,

What I believe is that the receptacle face is rated for 15 amps at that receptacle, however you are allowed to let a 20 amp load pass through the GFI receptacle. You could find 20 amp GFI rated receptacles which also allow 20 amp feed through. The NEC also allows 15 amp receptacles on a 20 amp circuit because there is a duplex outlet. If however you only installed 1 recptacle outlet on a 20 amp receptacle, then it would have to be rated for 20 amps. We use to call the 20 amp recptacles "T" rated, because of the "T" shaped slots.

Harold


#18842 - 12/15/02 09:09 PM Re: Question About Receptacles  
ThinkGood  Offline
Member
Joined: Aug 2002
Posts: 1,081
Milwaukee, WI
Thanks, all, for the replies. I thought that it was probably a matter of just the face of the receptacle rather than the "guts."

Mr. Endean: Are you referring to these?
[Linked Image]

Electric ed: I saw one photo here with the cover that had shorted a plug. That was enough to convince me.

classicsat: dissecting GFCIs sounds like fun, just as long as nobody got hurt. What caused it to become "spent?" I keep hearing about the low-quality models not lasting long and/or not working properly. We're talking LIVES here, Mr./Ms. Manufacturer!!!


#18843 - 12/15/02 09:54 PM Re: Question About Receptacles  
spyder  Offline
Member
Joined: Oct 2002
Posts: 210
Massachusetts
Where do you get your great clipart?


#18844 - 12/15/02 10:47 PM Re: Question About Receptacles  
ThinkGood  Offline
Member
Joined: Aug 2002
Posts: 1,081
Milwaukee, WI
Thank you. I was into web development until I got "downsized." I grab from here and there on the non copyrighted stuff, and then combine it as needed. Feel free to grab any of it.

'Lectric was always a hobby of mine. I am very serious about pursuing a career in the field. Trouble is that "experience needed" I see in the want ads. I am hoping to get over to the union as soon as some documentation comes in to show that I took algebra in school.

I know I can't save the world but I would like to make a difference. I am soaking in a whole lot of knowledge here and I can tell the difference between the professionals here and people with whom I have talked on the telephone or in person, who are just out to make a quick buck.

[This message has been edited by ThinkGood (edited 12-15-2002).]


#18845 - 12/16/02 12:11 PM Re: Question About Receptacles  
classicsat  Offline
Member
Joined: Nov 2002
Posts: 456
Lightning or someting blew the transistor that engaged the tripping solenoid.


#18846 - 12/16/02 01:07 PM Re: Question About Receptacles  
BuggabooBren  Offline
Member
Joined: Nov 2001
Posts: 328
NM
I have wondered if this topic would resurface - Which way is up? I also thought of a solution - either way could be up if the receptacles were slightly changed. Are there reasons (grounding, code, etc?) why this wouldn't work? (sending image to ECN & will correct link asap)

[This message has been edited by BuggabooBren (edited 12-16-2002).]


Page 1 of 2 1 2

Member Spotlight
Scott35
Scott35
Anaheim, CA. USA
Posts: 2,707
Joined: October 2000
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 15 (0.003s) Memory: 0.8178 MB (Peak: 0.9919 MB) Zlib enabled. Server Time: 2017-07-22 14:49:25 UTC