A Tamper Resistant Brain Teaser #187997
07/16/09 09:55 PM
07/16/09 09:55 PM
HotLine1  Offline
OP
Member
Joined: Apr 2002
Posts: 6,916
Brick, NJ USA
From 2008 NEC:

"406.11 Tamper-Resistant Receptacles in Dwelling Units.
In all areas specified in 210.52, all 125-volt, 15- and 20-ampere receptacles shall be listed tamper-resistant receptacles."

Now...

What say you regarding a L5-15 or L5-20 twistlock installed inside a resi?




John
2017 / 2014 NEC & Related Books and Study Guides
Re: A Tamper Resistant Brain Teaser [Re: HotLine1] #187998
07/16/09 10:05 PM
07/16/09 10:05 PM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,263
Fullerton, CA USA

bash clap

I'd say that it effectively prohibits Twistlocks in resi.




Re: A Tamper Resistant Brain Teaser [Re: HotLine1] #187999
07/16/09 10:05 PM
07/16/09 10:05 PM
E
EV607797  Offline
Member
Joined: Oct 2006
Posts: 745
Fredericksburg, VA, USA
I'm an electrical geek and I have a few Twistlock receptacles in my house for battery backup system connections. I guess I won't be allowed to do that anymore! cry


---Ed---

"But the guy at Home Depot said it would work."
Re: A Tamper Resistant Brain Teaser [Re: EV607797] #188073
07/20/09 09:56 PM
07/20/09 09:56 PM
S
sparkyinak  Offline
Member
Joined: Jul 2007
Posts: 1,328
Alaska
As an inspector, I would ask, "What are they needed for?" The only UPS's I know are are commerical grade UPS units you would find in an IT room. Even the ones used at my office have just a standand NEMA 5-15 plug. If it is needed for a home office then the dwelling can become a mixed occupancy. This is a double edge swords since mixed occupancies must meet other code requirements too. Such as floor loading, fire protection, etc. If someone were to go this route best be up on their local appicable codes.


"Live Awesome!" - Kevin Carosa
Re: A Tamper Resistant Brain Teaser [Re: sparkyinak] #188076
07/20/09 10:35 PM
07/20/09 10:35 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,166
Estero,Fl,usa
If they are in addition to the ones specified by 210.52 it is not clear they have to be T/R.

Quote
406.11 Tamper-Resistant Receptacles in Dwelling Units.
In all areas specified in 210.52, all 125-volt, 15- and 20-ampere receptacles shall be listed tamper-resistant receptacles.



You have to be careful how you answer that or we will be looking for a T/R twist lock for the A/G pool pump.


Greg Fretwell
Re: A Tamper Resistant Brain Teaser [Re: gfretwell] #188078
07/20/09 10:50 PM
07/20/09 10:50 PM
HotLine1  Offline
OP
Member
Joined: Apr 2002
Posts: 6,916
Brick, NJ USA
Greg:

'...in all areas specified....' NOT '....to the ones specified.....'
Good thought, but not exactly what the book says.


SparkyinAK:

As an inspector...I can't ask 'what are they needed for'. BTW, this is a theoretical brain teaser.



John
Re: A Tamper Resistant Brain Teaser [Re: HotLine1] #188079
07/21/09 01:12 AM
07/21/09 01:12 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,166
Estero,Fl,usa
I just don't like the way 406.11 is worded I guess.
"outdoors" is "specified" in 210,52(E) but it doesn't apply to all receptacles outdoors.
If it doesn't apply to the receptacle on a pool pump outdoors, why would it apply to a receptacle indoors that is not specified in 210.52,

Quote
210.52 Dwelling Unit Receptacle Outlets.
This section provides requirements for 125-volt, 15- and 20-ampere receptacle outlets. The receptacles required by this section shall be in addition to any receptacle that is:
(1) Part of a luminaire or appliance, or
(2) Controlled by a wall switch in accordance with 210.70(A)(1), Exception No. 1, or
(3) Located within cabinets or cupboards, or
(4) Located more than 1.7 m (51/2 ft) above the floor


Since these are not specified in 210.52 are they exempt?


Greg Fretwell
Re: A Tamper Resistant Brain Teaser [Re: gfretwell] #188099
07/21/09 02:15 PM
07/21/09 02:15 PM
HotLine1  Offline
OP
Member
Joined: Apr 2002
Posts: 6,916
Brick, NJ USA
Greg:
IMHO, 210.52 is the 'required' receptacle outlets, detailing required spacing, locations, etc. Basically, the code required minimums.

Yes, 406.11 wording is not liked by a few people.





John
Re: A Tamper Resistant Brain Teaser [Re: HotLine1] #188107
07/21/09 05:16 PM
07/21/09 05:16 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,166
Estero,Fl,usa
That was my point. If a receptacle is not one of the ones required by 210.52 is it required to be TR?
The examples would be the ones I referenced in the first paragraph of 210.52 that are "in addition" to the ones "specified" in 201.52.
That would certainly exempt the garage door receptacle for example. Also I doubt you would have to use TR in the appliance garage. The real question left open is the switch controlled lighting outlets.

Do the manufacturers have TR receptacles in baseboard heaters?


Greg Fretwell
Re: A Tamper Resistant Brain Teaser [Re: gfretwell] #188109
07/21/09 06:47 PM
07/21/09 06:47 PM
HotLine1  Offline
OP
Member
Joined: Apr 2002
Posts: 6,916
Brick, NJ USA
Greg:

Commentary at CEU course on '08 changes leaned toward the word 'all' for TR recept's.

Discussing this here with you has me thinking about the commentary that was part of the changes presentation materials.

We (NJ) have until 10/1/09 to get our 'act' together on a few items, this being one.

I'm going into this with an open mind, and now...going to dig out the 'changes' commentary that we used....hopefully it's in my files, not 'loaned' & never returned!

As to the BB htrs.....more food for thought.



John
Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
electure
electure
Fullerton, CA USA
Posts: 4,263
Joined: December 2000
Show All Member Profiles 
Top Posters(30 Days)
sparky 23
Admin 20
Potseal 13
Popular Topics(Views)
243,516 Are you busy
180,314 Re: Forum
170,811 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.020s Queries: 16 (0.004s) Memory: 1.0271 MB (Peak: 1.2084 MB) Zlib enabled. Server Time: 2018-01-17 13:09:26 UTC