Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
From 2008 NEC:

"406.11 Tamper-Resistant Receptacles in Dwelling Units.
In all areas specified in 210.52, all 125-volt, 15- and 20-ampere receptacles shall be listed tamper-resistant receptacles."

Now...

What say you regarding a L5-15 or L5-20 twistlock installed inside a resi?




John
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Dec 2000
Posts: 4,294
Member

bash clap

I'd say that it effectively prohibits Twistlocks in resi.




Joined: Oct 2006
Posts: 745
E
Member
I'm an electrical geek and I have a few Twistlock receptacles in my house for battery backup system connections. I guess I won't be allowed to do that anymore! cry


---Ed---

"But the guy at Home Depot said it would work."
Joined: Jul 2007
Posts: 1,335
S
Member
As an inspector, I would ask, "What are they needed for?" The only UPS's I know are are commerical grade UPS units you would find in an IT room. Even the ones used at my office have just a standand NEMA 5-15 plug. If it is needed for a home office then the dwelling can become a mixed occupancy. This is a double edge swords since mixed occupancies must meet other code requirements too. Such as floor loading, fire protection, etc. If someone were to go this route best be up on their local appicable codes.


"Live Awesome!" - Kevin Carosa
Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
If they are in addition to the ones specified by 210.52 it is not clear they have to be T/R.

Quote
406.11 Tamper-Resistant Receptacles in Dwelling Units.
In all areas specified in 210.52, all 125-volt, 15- and 20-ampere receptacles shall be listed tamper-resistant receptacles.



You have to be careful how you answer that or we will be looking for a T/R twist lock for the A/G pool pump.


Greg Fretwell
Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
Greg:

'...in all areas specified....' NOT '....to the ones specified.....'
Good thought, but not exactly what the book says.


SparkyinAK:

As an inspector...I can't ask 'what are they needed for'. BTW, this is a theoretical brain teaser.



John
Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
I just don't like the way 406.11 is worded I guess.
"outdoors" is "specified" in 210,52(E) but it doesn't apply to all receptacles outdoors.
If it doesn't apply to the receptacle on a pool pump outdoors, why would it apply to a receptacle indoors that is not specified in 210.52,

Quote
210.52 Dwelling Unit Receptacle Outlets.
This section provides requirements for 125-volt, 15- and 20-ampere receptacle outlets. The receptacles required by this section shall be in addition to any receptacle that is:
(1) Part of a luminaire or appliance, or
(2) Controlled by a wall switch in accordance with 210.70(A)(1), Exception No. 1, or
(3) Located within cabinets or cupboards, or
(4) Located more than 1.7 m (51/2 ft) above the floor


Since these are not specified in 210.52 are they exempt?


Greg Fretwell
Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
Greg:
IMHO, 210.52 is the 'required' receptacle outlets, detailing required spacing, locations, etc. Basically, the code required minimums.

Yes, 406.11 wording is not liked by a few people.





John
Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
That was my point. If a receptacle is not one of the ones required by 210.52 is it required to be TR?
The examples would be the ones I referenced in the first paragraph of 210.52 that are "in addition" to the ones "specified" in 201.52.
That would certainly exempt the garage door receptacle for example. Also I doubt you would have to use TR in the appliance garage. The real question left open is the switch controlled lighting outlets.

Do the manufacturers have TR receptacles in baseboard heaters?


Greg Fretwell
Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
Greg:

Commentary at CEU course on '08 changes leaned toward the word 'all' for TR recept's.

Discussing this here with you has me thinking about the commentary that was part of the changes presentation materials.

We (NJ) have until 10/1/09 to get our 'act' together on a few items, this being one.

I'm going into this with an open mind, and now...going to dig out the 'changes' commentary that we used....hopefully it's in my files, not 'loaned' & never returned!

As to the BB htrs.....more food for thought.



John