#170435 - 11/02/07 09:22 PM 12/4 in computer rooms  
frank  Offline
Member
Joined: May 2001
Posts: 376
windsor ontario canada
Can 12/4 be ran from three phase panels for normal and standard emergency recepticals in a computer room?
thanks


Tools for Electricians:

#170440 - 11/02/07 10:50 PM Re: 12/4 in computer rooms [Re: frank]  
SP4RX  Offline
Member
Joined: Oct 2007
Posts: 56
Edmonton, Alberta, Canada...eh
What exactly are "normal and standard emergency receptacles"? And I don't think I've seen any reference to computer rooms in the code book.


Shawn.


#170441 - 11/02/07 11:22 PM Re: 12/4 in computer rooms [Re: SP4RX]  
wacked  Offline
Member
Joined: Dec 2006
Posts: 33
Are you referring to two different sources ( normal from hydro and standby, from say a UPS or a genset) inside a common piece of cable such as 12/4 bx cable?


#170471 - 11/03/07 08:52 PM Re: 12/4 in computer rooms [Re: wacked]  
frank  Offline
Member
Joined: May 2001
Posts: 376
windsor ontario canada
It's a hospital so the equipment is on both generator and UPS.Would 12/4 or any 4 conductor ac90 be legal on general purpose recepticals from 3 phase panels.I have only used it for 3 phase 4 wire equipment not plugs.I'm thinking the neutral could possibly end up being to small.The 12/4 comes from the panel to a j-box where they split into circiuts.Not the way i would do it but if it passes so be it.
thanks


#170517 - 11/05/07 01:06 AM Re: 12/4 in computer rooms [Re: frank]  
wacked  Offline
Member
Joined: Dec 2006
Posts: 33
What you have is an emergency panel feeding a UPS that feeds to outlet in a server room??? Three hots and a neutral for plugs. I don't think it is illegal as per the Canadian Electrical Code to do that unless the circuits are in a intermediate and critical care area (24-110) That said, any recent wiring I have seen done in healthcare facilities all seem to use a hot and a dedicated common labelled as such for each hot. (two wire circuits)


#170536 - 11/05/07 01:31 PM Re: 12/4 in computer rooms [Re: frank]  
jay8  Offline
Member
Joined: Jul 2005
Posts: 183
Vancouver, BC
You can do it, but with harmonic producing loads such as that found in computer rooms, you are better off with a separate neutral for each circuit. Certain harmonics can load up the neutral beyond the ampacity of a single circuit.



Member Spotlight
NickD
NickD
Amish Country, PA
Posts: 46
Joined: March 2013
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.027s Queries: 15 (0.005s) Memory: 0.7748 MB (Peak: 0.9216 MB) Zlib enabled. Server Time: 2017-10-23 04:25:40 UTC