12/4 in computer rooms #170435
11/02/07 09:22 PM
11/02/07 09:22 PM
F
frank  Offline OP
Member
Joined: May 2001
Posts: 376
windsor ontario canada
Can 12/4 be ran from three phase panels for normal and standard emergency recepticals in a computer room?
thanks

Tools for Electricians:
Re: 12/4 in computer rooms [Re: frank] #170440
11/02/07 10:50 PM
11/02/07 10:50 PM
S
SP4RX  Offline
Member
Joined: Oct 2007
Posts: 56
Edmonton, Alberta, Canada...eh
What exactly are "normal and standard emergency receptacles"? And I don't think I've seen any reference to computer rooms in the code book.


Shawn.

Re: 12/4 in computer rooms [Re: SP4RX] #170441
11/02/07 11:22 PM
11/02/07 11:22 PM
W
wacked  Offline
Member
Joined: Dec 2006
Posts: 33
Are you referring to two different sources ( normal from hydro and standby, from say a UPS or a genset) inside a common piece of cable such as 12/4 bx cable?

Re: 12/4 in computer rooms [Re: wacked] #170471
11/03/07 08:52 PM
11/03/07 08:52 PM
F
frank  Offline OP
Member
Joined: May 2001
Posts: 376
windsor ontario canada
It's a hospital so the equipment is on both generator and UPS.Would 12/4 or any 4 conductor ac90 be legal on general purpose recepticals from 3 phase panels.I have only used it for 3 phase 4 wire equipment not plugs.I'm thinking the neutral could possibly end up being to small.The 12/4 comes from the panel to a j-box where they split into circiuts.Not the way i would do it but if it passes so be it.
thanks

Re: 12/4 in computer rooms [Re: frank] #170517
11/05/07 01:06 AM
11/05/07 01:06 AM
W
wacked  Offline
Member
Joined: Dec 2006
Posts: 33
What you have is an emergency panel feeding a UPS that feeds to outlet in a server room??? Three hots and a neutral for plugs. I don't think it is illegal as per the Canadian Electrical Code to do that unless the circuits are in a intermediate and critical care area (24-110) That said, any recent wiring I have seen done in healthcare facilities all seem to use a hot and a dedicated common labelled as such for each hot. (two wire circuits)

Re: 12/4 in computer rooms [Re: frank] #170536
11/05/07 01:31 PM
11/05/07 01:31 PM
J
jay8  Offline
Member
Joined: Jul 2005
Posts: 183
Vancouver, BC
You can do it, but with harmonic producing loads such as that found in computer rooms, you are better off with a separate neutral for each circuit. Certain harmonics can load up the neutral beyond the ampacity of a single circuit.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
richard
richard
L.I. New York
Posts: 98
Joined: August 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 13
Trumpy 11
sparky 7
Popular Topics(Views)
249,350 Are you busy
187,284 Re: Forum
176,632 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.017s Queries: 15 (0.003s) Memory: 0.9754 MB (Peak: 1.1251 MB) Zlib enabled. Server Time: 2018-09-21 19:39:57 UTC