#169725 - 10/13/07 02:43 PM Large RV parK services  
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 834
Michigan
Large RV park Power Co. brings in several services off of several transformers in Different locations.(spread out over large area one owner) Each service allowed up to Six Switches without a main . One transformers feeds two areas . It feeds 2-800 amp services back to back. Six disconnects each ? As each is a service.
Since there all out in the open they are Not feeding buildings or Structures. Makes for an interesting question.
Opinions please.
YoopersUP


2017 / 2014 NEC & Related Books and Study Guides

#169730 - 10/13/07 06:10 PM Re: Large RV parK services [Re: Yoopersup]  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
The first thing to remember is that the NEC stops where the PoCo takes over. In most instances, we can consider the meter as this point.

So ... that would be six disconnects after each meter.

These are not to be confused with customer owned meters that there night be on each space.

If the meters at each pedestal are, in fact, PoCo meters, then the NEC does not apply to whatever feeds those meters.


#169732 - 10/13/07 08:10 PM Re: Large RV parK services [Re: renosteinke]  
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 834
Michigan
Theres Never Meters at each Pedestal , You;d have over 100 meters or so in the park. They usually CT at the transformer . Then run to the Main Pnl. But even then the Service point for Each is at the panel, But one transformer has two service drops Ct'd at the transformer.( RV) parKs are awhole different ball game.Remember this is a RV park not a Trailer Park.



Member Spotlight
JoeKP
JoeKP
Berkley, MA
Posts: 144
Joined: March 2008
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.013s Queries: 15 (0.002s) Memory: 0.7518 MB (Peak: 0.8774 MB) Zlib enabled. Server Time: 2017-11-19 14:16:46 UTC