Series breakers #167391
08/11/07 01:49 PM
08/11/07 01:49 PM
Niko  Offline OP
Member
Joined: Aug 2006
Posts: 356
Campbell, CA
The city electric plan checker needs the following on the plans: DOCUMENTATION REGARDING SERIES BREAKERS :

This was the list that was given to me by the building owner i was not available to ask the plan checker what he meant by series breaker documentation

Can you guys tell me what he means?

Thank you.


Be kind to your neighbor, he knows where you live

Work Gear for Electricians and the Trades
Re: Series breakers [Re: Niko] #167399
08/11/07 08:05 PM
08/11/07 08:05 PM
J
jraef  Offline
Member
Joined: Jul 2004
Posts: 101
San francisco, CA, USA
When you have one breaker used upstream of others, they all must be listed (by UL) for use in series, i.e. the let-through of the upstream breaker is lower than the withstand of the downstream ones. If they are in a panelboard and all are the same make, you should be able to get that info from the manufacturer now. If you have mixed brands within a panelboard or are using stand-alone breakers, you may have to pay a PE to do a certified coordination study on them.


JRaef
Re: Series breakers [Re: jraef] #167403
08/11/07 09:26 PM
08/11/07 09:26 PM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
I'm not sure I understand that explanation.

"Selective co-ordination" is one thing.

I really can't accept the implied requirement that every panel and disconnect be of the same make as the main switchgear.

I think we still need a better explanation of 'series rating,' and when it is relevant.

Re: Series breakers [Re: renosteinke] #167406
08/11/07 10:58 PM
08/11/07 10:58 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,166
Estero,Fl,usa
This might be helpful. Poke around the search box for a few more articles from the magazine


Greg Fretwell
Re: Series breakers [Re: renosteinke] #167407
08/11/07 10:58 PM
08/11/07 10:58 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Series rating applies when you are installing a downsteam breaker that has a lower interrupting rating than the available fault current at that point on the circuit. It is the only way you can make that type of installation.
Quote
I really can't accept the implied requirement that every panel and disconnect be of the same make as the main switchgear.

In general a series rating is only obtained by testing. Manufacturer A does not have their breakers tested in combination with other brands. This restriction only applies when you are using a series rating.
Don


Don(resqcapt19)
Re: Series breakers [Re: resqcapt19] #167408
08/11/07 11:03 PM
08/11/07 11:03 PM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Thank you, Don, for straightening out an issue that is confused enough ...

Re: Series breakers [Re: renosteinke] #167415
08/12/07 02:06 AM
08/12/07 02:06 AM
Scott35  Offline

Broom Pusher and
Member
Joined: Oct 2000
Posts: 2,708
Anaheim, CA. USA
Niko:

Quote

The city electric plan checker needs the following on the plans:
: DOCUMENTATION REGARDING SERIES BREAKERS :

Can you guys tell me what he means?


What the Plans Examiner is requesting here is for Manufacturer's Spec documents, to be submitted to the Plan Check firm (in hard copy, or "printed" format), which are relavent to a Series Rated System.

These documents will list devices and equipment, that are acceptable to be installed within a Series Rated System. Manufacturer's part numbers + categories will be referenced, as to their use downstream of a given Service Section or Gear Section & OCPD.

If your System IS NOT Series Rated, then write in your reply to the Correction notice:
"This Electrical System Is Fully Rated, Not Series Rated", then submit the marked up correction list to the P/C firm (P/C = Plan Check).
Submit it, along with your contact information + note to have the P/C person contact you for further questions.

If the System is / will be Series Rated, then go to the Manufacturer's website, and printout / download "Cut-Sheets" for their approved combinations of equipment and devices usable on Series Rated Systems.

If you are unsure if the System is / is not Series Rated:
  1. Review the 1 Line Diagram + spec notes of the Planset, look for some indication of Series Rating,
    or,
  2. Verify the On-Site conditions - need to know the Fault Levels at Panelboards, Disconnects, Gear Sections and the Service Equipment.


Maybe there is a high fault level indicated at a remote Panelboard ( > 10KAIC ), which drew attention to the P/C during the exam - and this is why they request the documents.

If this project is Design / Build, and you are the designer, you _should_ know if the System is / will be Series Rated.

I include notes on the cover page, the 1 Line page, and the Panel Schedule page(s) which call out if a System is or is not Series Rated - as follows:

* This System Is a _FULLY RATED_ System (NOT Series Rated).
SCA levels at various points along the system do not exceed the AIR (AIC) of installed Overcurrent Devices or Panels.

or;

* This System Is _SERIES RATED_.
Supporting documents are attached to this Planset, and will be submitted as separate documents - in addition to this Planset - for Plan Examination.
Overcurrent Devices, Panelboards, Service Equipment and other related Equipment intended for use in a Series Rated fashion, have been listed in the Materials Specifications list of this Planset, and have been identified at points on the 1 Line Diagram(s).

Scott


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Re: Series breakers [Re: Scott35] #167483
08/13/07 09:30 AM
08/13/07 09:30 AM
Niko  Offline OP
Member
Joined: Aug 2006
Posts: 356
Campbell, CA
Thank you gentelman for the detailed explanation.
I learned something today.


Be kind to your neighbor, he knows where you live


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
waymag
waymag
dallas, texas, USA
Posts: 67
Joined: January 2002
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 16
Potseal 15
Popular Topics(Views)
243,576 Are you busy
180,374 Re: Forum
170,852 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.023s Queries: 15 (0.004s) Memory: 0.9965 MB (Peak: 1.1576 MB) Zlib enabled. Server Time: 2018-01-21 14:31:50 UTC