Rcd trip times #143916
09/16/05 01:00 PM
09/16/05 01:00 PM
A
aland  Offline OP
Member
Joined: May 2004
Posts: 186
United Kingdom
Anybody have any extensive experience with
testing and inspection?
On a number of occasions over the years have tested Rcd's for compliance with trip times and found that the trip time registered at 30ma is faster than that at 150ma. Use a Chauvin Arnoux 6115 installation tester calibrated anually by the manufacturer. This has occured on all sorts of different makes of rcd's over time.
Anyone else ever experienced anything like it? Todays test was on a Federal GFI 30ma trip. Test at 30ma 12.4ms test at 150ma 32.8ms. Thoughts gentlemen please!

Test Equipment:
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Re: Rcd trip times #143917
09/17/05 02:24 AM
09/17/05 02:24 AM
Trumpy  Offline

Member
Joined: Jul 2002
Posts: 8,231
SI,New Zealand
Gidday Alan,
I use an AVO Megger Installation tester to do my testing of RCD's.
I have seen these results pop up everytime I test.
Over here it has to be under 300mS trip time
at the stated (say 30mA) current.
I think the longest time I have had is 42mS, and that was at 300mA, with a Selective RCD.

Re: Rcd trip times #143918
09/17/05 10:10 AM
09/17/05 10:10 AM
P
pauluk  Offline
Member
Joined: Aug 2001
Posts: 7,520
Norfolk, England
It's interesting to tryand figure out why the breaker should take longer to trip at the higher current.

I'm thinking along the lines of hyteresis in the core maybe? It's quite a difference though -- After all, a full-cycle of 50Hz is 20mS.



[This message has been edited by pauluk (edited 09-17-2005).]

Re: Rcd trip times #143919
09/25/05 04:21 AM
09/25/05 04:21 AM
Trumpy  Offline

Member
Joined: Jul 2002
Posts: 8,231
SI,New Zealand
Guys,
I'm right into a thing like this.
Considering that my training teaches me that an RCD should trip quicker, with a higher amount of current.
If it was in fact Hysteresis I'd be worried by that.
If it took time to saturate the core of the RCD transformer, it could concievably kill someone.
An experiment to do at work in the weekend!. [Linked Image]

Re: Rcd trip times #143920
09/25/05 05:02 AM
09/25/05 05:02 AM
M
marcspages  Offline
Member
Joined: Oct 2004
Posts: 48
London, UK
Hi guys,

During power restoration (either the RCD being turned on again or the power being reapplied after an outage), there is usually a small amount of Earth inrush as power is seldom applied at the zero crossing of the waveform (not to mention that Live often connects first followed by the Neutral!). This inrush resulting from the natural (and unnatural) capacitance existing on the system.

RCDs need to ignore such inrush else one would simply never be able to restore power to a circuit (many who remember the very early RCDs will remember this problem especially as the "cure" was to trip all sub circuits, restore the main supply, and then, with fear, reenergise each circuit in turn praying the RCD would remain on!).

This anti-inrush-tripping is very simply achieved in the "non-electronic" versions by having two secondary windings on the RCD core. The first winding powers the operating solenoid (as shown in most explanations on RCDs). The second winding also feeds the solenoid, but is wired in reverse (i.e. the two windings cancel each other out). However, the second winding is fed via diodes and a capacitor meaning the solenoid can only operate once the capacitor has charged and thus removes the cancelling current.

At low currents the capacitor has very little charging to do as well as the diodes, because they have voltage drop, allow most of the main secondary current to flow in the solenoid with little cancelling current being allowed through - hence the faster operating times at lower currents.

Make sense?

M.

Re: Rcd trip times #143921
09/25/05 05:28 AM
09/25/05 05:28 AM
P
pauluk  Offline
Member
Joined: Aug 2001
Posts: 7,520
Norfolk, England
Ah...... It's beginning to make sense. I've never really looked at the detailed arrangements of RCDs before.

How exactly are the diodes arranged on that extra winding? Is it a simple bridge rectifier followed by a series capacitor?

Re: Rcd trip times #143922
09/25/05 12:12 PM
09/25/05 12:12 PM
A
aland  Offline OP
Member
Joined: May 2004
Posts: 186
United Kingdom
Thanks for the explanation M. All sounds very plausible.
Why does this only happen on odd occasions then? Have asked the question of Chauvin Arnoux! no satisfactory answer as yet.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 16
Potseal 15
Popular Topics(Views)
243,561 Are you busy
180,362 Re: Forum
170,840 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.015s Queries: 14 (0.004s) Memory: 0.9844 MB (Peak: 1.1369 MB) Zlib enabled. Server Time: 2018-01-20 10:58:26 UTC