#129220 - 11/02/04 02:44 AM Unbalanced delta calculations  
u2slow  Offline
Member
Joined: Sep 2003
Posts: 200
Salt Spring, BC, Canada
I'm in 3rd year school right now, and some of the 3-phase math is getting me down... unbalanced delta loads specifically - trying to figure out the line currents.

Our instructor's method works but the values he chooses and when he uses them seems arbitrary. Put the wrong two phasors head to tail, and the resultant in meaningless.

Anyone have some tips or tricks?


Tools for Electricians:

#129221 - 11/06/04 10:14 PM Re: Unbalanced delta calculations  
crash  Offline
Member
Joined: Oct 2003
Posts: 147
Calgary Canada
There are no "Tricks" in 3 phase, phasor calculations. Just math.

Can You post a specific problem with (or with-out) your instructors solution? And also what your instructor choose in an "arbitrary" manor?


#129222 - 11/07/04 12:01 AM Re: Unbalanced delta calculations  
u2slow  Offline
Member
Joined: Sep 2003
Posts: 200
Salt Spring, BC, Canada
I figured it out [Linked Image] (Thanks for responding!)

My instructor was busy disecting each phasor into X and Y values with sin/cos functions and subtracting them. It just didn't make sense until he showed what he was doing with a phasor diagram and finally had a 3-blade propellor drawn on the board. *Now* that made a whole lot more sense! I worked through a few more problems with the diagrams only... and solved them all. Now the original purely-arithmetic method is starting to make sense. Go figure [Linked Image]

What I found arbitrary was how he assigned the A, B, & C phase subscripts to the current phasors. I now know it doesn't matter - you get same answers no matter how you do it. [Linked Image]

Here is one of the problems. I'll see if I can transcribe the solution and post it up.

Q:

The phase currents in a delta-connected, unbalanced load are 20A, 32A, and 40A. Calculate the three line currents, if all loads are resistors.

A:

52.92A, 62.35A, 45.43A


#129223 - 11/08/04 02:13 AM Re: Unbalanced delta calculations  
crash  Offline
Member
Joined: Oct 2003
Posts: 147
Calgary Canada
I got the same answers as you on that problem. It took a little while for me to remember how to do it though.


#129224 - 11/09/04 11:50 PM Re: Unbalanced delta calculations  
Peter  Offline
Member
Joined: Jun 2004
Posts: 92
San Diego
I am confused here. What is the equation? I thought it would be amps times the square root of three.
~Peter



Member Spotlight
Bill Addiss
Bill Addiss
NY, USA
Posts: 3,878
Joined: October 2000
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.016s Queries: 14 (0.003s) Memory: 0.7674 MB (Peak: 0.9048 MB) Zlib enabled. Server Time: 2017-10-20 07:16:08 UTC