Joined: Sep 2003
Posts: 200
U
u2slow Offline OP
Member
I'm in 3rd year school right now, and some of the 3-phase math is getting me down... unbalanced delta loads specifically - trying to figure out the line currents.

Our instructor's method works but the values he chooses and when he uses them seems arbitrary. Put the wrong two phasors head to tail, and the resultant in meaningless.

Anyone have some tips or tricks?

Joined: Oct 2003
Posts: 147
C
Member
There are no "Tricks" in 3 phase, phasor calculations. Just math.

Can You post a specific problem with (or with-out) your instructors solution? And also what your instructor choose in an "arbitrary" manor?

Joined: Sep 2003
Posts: 200
U
u2slow Offline OP
Member
I figured it out [Linked Image] (Thanks for responding!)

My instructor was busy disecting each phasor into X and Y values with sin/cos functions and subtracting them. It just didn't make sense until he showed what he was doing with a phasor diagram and finally had a 3-blade propellor drawn on the board. *Now* that made a whole lot more sense! I worked through a few more problems with the diagrams only... and solved them all. Now the original purely-arithmetic method is starting to make sense. Go figure [Linked Image]

What I found arbitrary was how he assigned the A, B, & C phase subscripts to the current phasors. I now know it doesn't matter - you get same answers no matter how you do it. [Linked Image]

Here is one of the problems. I'll see if I can transcribe the solution and post it up.

Q:

The phase currents in a delta-connected, unbalanced load are 20A, 32A, and 40A. Calculate the three line currents, if all loads are resistors.

A:

52.92A, 62.35A, 45.43A

Joined: Oct 2003
Posts: 147
C
Member
I got the same answers as you on that problem. It took a little while for me to remember how to do it though.

Joined: Jun 2004
Posts: 92
P
Member
I am confused here. What is the equation? I thought it would be amps times the square root of three.
~Peter


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
togol
togol
NW In. USA
Posts: 421
Joined: September 2005
Top Posters(30 Days)
BigB 3
triple 2
Popular Topics(Views)
305,112 Are you busy
233,510 Re: Forum
218,193 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5