#118061 - 08/02/04 10:53 PM Hot Neutral  
Admin  Offline

Administrator
Member
Joined: Oct 2000
Posts: 3,447
NY, USA
Quote
Found this service with the neutral and phase conductors reversed in the meter base while performing a final inspection on a single family dwelling.

- necbuff
[Linked Image]

[Linked Image]


Tools for Electricians:

#118062 - 08/03/04 01:39 AM Re: Hot Neutral  
Lostazhell  Offline
Member
Joined: Feb 2004
Posts: 1,431
Bakersfield, CA (Originally Or...
Aside from the darwin award for not even being able to wire a meter socket, Please tell me thats not a bare AL ground wire going right in front of the main lugs for the panel?!?!?!? [Linked Image]

-Randy

[This message has been edited by Lostazhell (edited 08-03-2004).]


#118063 - 08/03/04 02:05 AM Re: Hot Neutral  
Big Jim  Offline
Member
Joined: Jul 2003
Posts: 394
Denver, CO USA
I think most 3 year-olds can match colors better than that. Things we do totally without concious thought are far beyond some people.


#118064 - 08/03/04 03:05 AM Re: Hot Neutral  
NORCAL  Offline
Member
Joined: Sep 2002
Posts: 872
Good panel, sloppy "work".


#118065 - 08/03/04 03:16 AM Re: Hot Neutral  
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
Is this service live?!!!!

No ground or bond between the meter and main, so the main case and neutral is 120, and one phase 0, the other 220?

Looks like some smoke damage there on the riser neutral?

This may not have happened if this person hadn't gone through all the "red tape" getting it inspected. Nice catch, and a real good thing you looked!


Mark Heller
"Well - I oughta....." -Jackie Gleason

#118066 - 08/03/04 01:41 PM Re: Hot Neutral  
electricman2  Offline
Member
Joined: Nov 2003
Posts: 269
Thomasville, NC USA
The GEC in pipe is nice although I dont understand the gap between end of pipe and meter can.


John

#118067 - 08/03/04 09:59 PM Re: Hot Neutral  
necbuff  Offline
Member
Joined: Jul 2004
Posts: 41
Lebanon Tn USA
Service not energized, I am AHJ and I obviously rejected this one. That is an insulated conductor in front of the lugs and the reason for the gap is for other utilites to have a spot to hit the GEC for their service, eg; catv, phone.


Kenny Wilee


Member Spotlight
mxslick
mxslick
Atomic City, ID USA
Posts: 803
Joined: October 2004
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.014s Queries: 14 (0.003s) Memory: 0.7841 MB (Peak: 0.9359 MB) Zlib enabled. Server Time: 2017-07-21 18:47:02 UTC