Measurement Starts From Face of Meter! #104277
01/20/03 06:42 PM
01/20/03 06:42 PM
Joe Tedesco  Offline OP
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
[Linked Image]

The working space clearance to show complianace with Table 110.26 starts from the face of the meter.

This space is inadequate and violates the code!!


[This message has been edited by Joe Tedesco (edited 09-10-2003).]


Joe Tedesco, NEC Consultant
2017 / 2014 NEC & Related Books and Study Guides
Re: Measurement Starts From Face of Meter! #104278
01/20/03 08:43 PM
01/20/03 08:43 PM
G
Gwz  Offline
Member
Joined: Apr 2002
Posts: 197
Zero Lot Lines ?

Dosen't look like the large switch door will open 90ยบ either.

Which premise is "at fault" ?

Re: Measurement Starts From Face of Meter! #104279
01/21/03 01:32 PM
01/21/03 01:32 PM
T
txsparky  Offline
Member
Joined: May 2001
Posts: 552
Magnolia,.Texas U.S.A.
We have 1 real similar to this in Conroe,Texas.But the building belongs to the mayor so apparently it is code compliant [Linked Image]


Donnie
Re: Measurement Starts From Face of Meter! #104280
01/21/03 07:14 PM
01/21/03 07:14 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,916
Brick, NJ USA
Joe:
Take that same type of alley, and put the left buildings service drop & meter there; along with the right buildings.
(It's in NJ, and the utility apparently "OK'd" it.)

I believe the local AHJ (not me) gave a "variance", as it's an old neighborhood
and the lots are tight.
John

[This message has been edited by HotLine1 (edited 01-21-2003).]


John
Re: Measurement Starts From Face of Meter! #104281
02/24/03 05:36 AM
02/24/03 05:36 AM
Joe Tedesco  Offline OP
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Another situation .... when standing in front of these disconnects what standing postion is the recommended practice?

To the left, or to the right, right handed or left handed?

In many cases the clearances for the handle are not even enough for a hand to grasp the handle so it can be operated!


Joe Tedesco, NEC Consultant
Re: Measurement Starts From Face of Meter! #104282
02/24/03 11:21 AM
02/24/03 11:21 AM
C
Creighton  Offline
Member
Joined: Jan 2002
Posts: 59
Hayward, CA
Joe: I hate to differ with you, but 110.26(A)(1)says the depth of the working space is measured from the face of the enclosure,, not the face of the meter. Creighton

Re: Measurement Starts From Face of Meter! #104283
02/24/03 11:47 AM
02/24/03 11:47 AM
Joe Tedesco  Offline OP
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Hello Creighton:

You are correct. I was stretching the point while reading the first words in the definition of "Enclosure" in Article 100 .......

Quote
Enclosure. The case or housing of apparatus, or .....


I personally believe that the face of the meter itself does entroach into the working space.

The meter reader will have to slide by the space in the front of the glass to stand in front of it to read the meter, and some meter readers may even touch the glass with their nose if they are a size 36 like I am...


Joe Tedesco, NEC Consultant
Re: Measurement Starts From Face of Meter! #104284
02/24/03 02:06 PM
02/24/03 02:06 PM
E
elecRB  Offline
Junior Member
Joined: Oct 2002
Posts: 4
Loveland CO USA
Even with my bifocals I couldn't stand that close to that equipment and read the nameplate data much less do any work.

Just think -- an electrical arc blast reaches 35,000 degrees F and standing in front of that equipment you become the middle of the sandwich!

Re: Measurement Starts From Face of Meter! #104285
02/25/03 12:07 AM
02/25/03 12:07 AM
F
frenchelectrican  Offline
Member
Joined: Feb 2003
Posts: 939
Wi/ Paris France { France for ...
something like this what i genrall do is stay on the right side of disconnet switch and use my left hand to oprate and face away from door and forewarn any one near the area to say "engerizeing box " or juice on soon "

but few other may have diffren way please do let us know i hope i can find a better and safer way with the encloseres boxes

merci marc


Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)

Re: Measurement Starts From Face of Meter! #104286
02/25/03 01:59 PM
02/25/03 01:59 PM
T
ThinkGood  Offline
Member
Joined: Aug 2002
Posts: 1,081
Milwaukee, WI
I don't believe there is a safe way to operate the switch here as one has to be almost on top of it in order to operate it!


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
MarkC10
MarkC10
CA, Inland Empire
Posts: 43
Joined: September 2013
Show All Member Profiles 
Top Posters(30 Days)
sparky 24
Admin 19
Potseal 13
Popular Topics(Views)
243,508 Are you busy
180,293 Re: Forum
170,798 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.061s Queries: 14 (0.020s) Memory: 1.0095 MB (Peak: 1.1864 MB) Zlib enabled. Server Time: 2018-01-16 09:52:07 UTC