#103152 - 05/02/02 02:41 AM Found When Sheetrock Was Removed  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Joe,

Please accept this as a code violation for "What's Wrong Here?"

Flexible cords and cables are not permitted as a substitute for fixed wiring and should not be concealed behind walls.

[Linked Image]

PHOTO FACTS

This photo shows an outlet that was uncovered within an office building when some sheetrock was removed during a major renovation project of the facility.

Please note that the building was purchased by a local University, and the electrical installation may have been done by the original owners.

I believe that this installation could be considered for several violations, but I have
chosen NEC 400-8 (1) and (5).

Dennis L. Ferguson


Joe Tedesco, NEC Consultant

2017 / 2014 NEC & Related Books and Study Guides

#103153 - 05/02/02 11:28 AM Re: Found When Sheetrock Was Removed  
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,878
NY, USA
Admitedly, I'm guessing here that one reason for rules regarding flexible cords has to do with deterioration of the insulation over time. I have seen cords where the (rubberized ?) insulation is at the point where it crumbles when touched. What are the worst types of conditions for flexible cords to be under? ... Hot & Dry?

Bill


#103154 - 05/14/02 11:39 PM Re: Found When Sheetrock Was Removed  
John Steinke  Offline
Member
Joined: Apr 2001
Posts: 518
Reno,Nv., USA
Bill,
I'd have to look at the UL testing protocols to speculate as to why (or when) romex and SO cord are/are not interchangeable. Off the top of my head, I suppose that, in most situations, using SO in place of a "permanent wiring method" is more of a technical violation than a true hazard. I think that the code section was meant to address the semi-permanent use of extension cords, etc., where more protected methods should be used. I'm only guessing.
As to rubber "crumbling;" this is usually the result of long-term exposure to ozone in the air. Acid in the air can also cause this.
Lest anyone think that I'm endorsing things like the one in the photo- I most certainly am not! I think the "temporary wiring" clause is abused enough as it is. Indeed, the more I work with Romex. MC, etc., the more I like bending pipe!


#103155 - 05/15/02 10:42 AM Re: Found When Sheetrock Was Removed  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
John,
I don't think that the jacket of the SO cord stands up over time. I am in the process of removing a DSC system control panel at a chemical plant. The power supplies were cord and plug connected with SO cord and the jackets are falling apart. The THWN and PVC jacketed control cables in the same panel are in perfect shape. The cords and other wiring is all about 12 years old. I would expect that the jacket of NM is PVC like the shielded cables and would stand up much better over time then the SO cord. It is not just the jacket on the SO cord that is crumbling, the insulation on the conductors is also in poor shape, even where it was protected by the outer jacket.
Don(resqcapt19)


Don(resqcapt19)

#103156 - 05/19/02 02:34 AM Re: Found When Sheetrock Was Removed  
ed-n6ec  Offline
Junior Member
Joined: May 2002
Posts: 2
Fullerton, Calif. USA
The sad part of a kludge installation like the one shown is that it is so easy to do it right, and probably cheaper than using that expensive HD 5-15P plug. Using an extension box and knockout cover on the wall, a short piece of 12-2 BX between the two boxes would work great, be easy to put together, and meet code. Ed.


#103157 - 05/25/02 09:18 PM Re: Found When Sheetrock Was Removed  
elektrikguy  Offline
Member
Joined: May 2002
Posts: 132
woodstock,ga,usa
ED, I was just wondering if you would wrap tape around the joints after conceiling joints on a wall? I hope you twist those wires REALLY good?


#103158 - 05/26/02 08:09 AM Re: Found When Sheetrock Was Removed  
Gwz  Offline
Member
Joined: Apr 2002
Posts: 197
No one has mentioned 314.29 [ 370-29 ] of the original box being accessible.

[This message has been edited by Gwz (edited 05-26-2002).]



Member Spotlight
Posts: 362
Joined: April 2003
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.014s Queries: 14 (0.003s) Memory: 0.7860 MB (Peak: 0.9361 MB) Zlib enabled. Server Time: 2017-07-27 04:46:56 UTC