Found When Sheetrock Was Removed #103152 05/02/02 02:41 AM
Joined: Oct 2000
Posts: 2,749
Joe Tedesco Offline OP
Member
Joe,

Please accept this as a code violation for "What's Wrong Here?"

Flexible cords and cables are not permitted as a substitute for fixed wiring and should not be concealed behind walls.

[Linked Image]

PHOTO FACTS

This photo shows an outlet that was uncovered within an office building when some sheetrock was removed during a major renovation project of the facility.

Please note that the building was purchased by a local University, and the electrical installation may have been done by the original owners.

I believe that this installation could be considered for several violations, but I have
chosen NEC 400-8 (1) and (5).

Dennis L. Ferguson


Joe Tedesco, NEC Consultant
2017 / 2014 NEC & Related Books and Study Guides
Re: Found When Sheetrock Was Removed #103153 05/02/02 11:28 AM
Joined: Oct 2000
Posts: 3,961
Bill Addiss Offline
Member
Admitedly, I'm guessing here that one reason for rules regarding flexible cords has to do with deterioration of the insulation over time. I have seen cords where the (rubberized ?) insulation is at the point where it crumbles when touched. What are the worst types of conditions for flexible cords to be under? ... Hot & Dry?

Bill


Bill
Re: Found When Sheetrock Was Removed #103154 05/14/02 11:39 PM
Joined: Apr 2001
Posts: 518
J
John Steinke Offline
Member
Bill,
I'd have to look at the UL testing protocols to speculate as to why (or when) romex and SO cord are/are not interchangeable. Off the top of my head, I suppose that, in most situations, using SO in place of a "permanent wiring method" is more of a technical violation than a true hazard. I think that the code section was meant to address the semi-permanent use of extension cords, etc., where more protected methods should be used. I'm only guessing.
As to rubber "crumbling;" this is usually the result of long-term exposure to ozone in the air. Acid in the air can also cause this.
Lest anyone think that I'm endorsing things like the one in the photo- I most certainly am not! I think the "temporary wiring" clause is abused enough as it is. Indeed, the more I work with Romex. MC, etc., the more I like bending pipe!

Re: Found When Sheetrock Was Removed #103155 05/15/02 10:42 AM
Joined: Nov 2000
Posts: 2,148
R
resqcapt19 Offline
Member
John,
I don't think that the jacket of the SO cord stands up over time. I am in the process of removing a DSC system control panel at a chemical plant. The power supplies were cord and plug connected with SO cord and the jackets are falling apart. The THWN and PVC jacketed control cables in the same panel are in perfect shape. The cords and other wiring is all about 12 years old. I would expect that the jacket of NM is PVC like the shielded cables and would stand up much better over time then the SO cord. It is not just the jacket on the SO cord that is crumbling, the insulation on the conductors is also in poor shape, even where it was protected by the outer jacket.
Don(resqcapt19)


Don(resqcapt19)
Re: Found When Sheetrock Was Removed #103156 05/19/02 02:34 AM
Joined: May 2002
Posts: 2
E
ed-n6ec Offline
Junior Member
The sad part of a kludge installation like the one shown is that it is so easy to do it right, and probably cheaper than using that expensive HD 5-15P plug. Using an extension box and knockout cover on the wall, a short piece of 12-2 BX between the two boxes would work great, be easy to put together, and meet code. Ed.

Re: Found When Sheetrock Was Removed #103157 05/25/02 09:18 PM
Joined: May 2002
Posts: 132
E
elektrikguy Offline
Member
ED, I was just wondering if you would wrap tape around the joints after conceiling joints on a wall? I hope you twist those wires REALLY good?

Re: Found When Sheetrock Was Removed #103158 05/26/02 08:09 AM
Joined: Apr 2002
Posts: 197
G
Gwz Offline
Member
No one has mentioned 314.29 [ 370-29 ] of the original box being accessible.

[This message has been edited by Gwz (edited 05-26-2002).]


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Potseal
Potseal
Saskatchewan
Posts: 264
Joined: February 2013
Show All Member Profiles 
Top Posters(30 Days)
BigB 2
Popular Topics(Views)
271,000 Are you busy
205,004 Re: Forum
193,122 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3