#102607 - 06/22/06 12:34 PM motor overloads  
jay8  Offline
Member
Joined: Jul 2005
Posts: 183
Vancouver, BC
I have a situation at work with a 10hp 600 volt motor driving a centrifugal pump. The 1.15 service factor of the motor allows us 125% for overload heater values, but can I continuously operate the motor at 125% of its nameplate value? In this case nameplate current is 9.4 amps, so 125% is 11.75 amps. The discharge valve of the pump is throttled back because wide open causes the motor to draw beyond its nameplate value. Thanks.


Tools for Electricians:

#102608 - 06/22/06 08:11 PM Re: motor overloads  
Rewired  Offline
Member
Joined: Jan 2006
Posts: 558
Hamilton, Ontario, Canada
I could be wrong but from what I have understood in the past the "service factor" is the percentage the motor can be overloaded for a SHORT DURATION without causing damage to the motor.. So really that motor will put out ( 10 * 1.15)= 11.5 horsepower ( 15% overload) for a short duration with no damage to the motor.. The overload heater being at 125% of nameplate FLA is just a MAXIMUM value of the setting of the overload heaters, not the percentage of how much you can overload the motor..

BTW, some overload heaters allow for the 125% rating.. you just size them to what your motor FLA is and thats it...should say somewhere on the overload or starter somewhere..

A.D


#102609 - 06/23/06 01:24 AM Re: motor overloads  
jay8  Offline
Member
Joined: Jul 2005
Posts: 183
Vancouver, BC
I pulled this definition from my old Cox's Electricians Guide to AC Motor Controls: service factor- the number by which the horsepower rating is multiplied to determine the maximum safe load that a motor may be expected to carry CONTINUOUSLY at its rated voltage and frequency."
Just curious if there any other thoughts out there.


#102610 - 06/26/06 06:50 PM Re: motor overloads  
Rewired  Offline
Member
Joined: Jan 2006
Posts: 558
Hamilton, Ontario, Canada
I picked up a handbook just now .. " IPT's electrical Handbook" and it says:

"Multiplying nameplate power by the service factor reflects how much the motor may be overloaded, PREFERABLY for brief periods"...
So I guess you could overload the motor continuously but it would shorten the life of the motor, as it is technically being run in an overloaded condition??!!

A.D



Member Spotlight
TOOL_5150
TOOL_5150
Bay Area
Posts: 61
Joined: August 2007
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.019s Queries: 14 (0.006s) Memory: 0.7591 MB (Peak: 0.8913 MB) Zlib enabled. Server Time: 2017-10-22 11:48:48 UTC