#102607 - 06/22/06 12:34 PM motor overloads  
jay8  Offline
Member
Joined: Jul 2005
Posts: 183
Vancouver, BC
I have a situation at work with a 10hp 600 volt motor driving a centrifugal pump. The 1.15 service factor of the motor allows us 125% for overload heater values, but can I continuously operate the motor at 125% of its nameplate value? In this case nameplate current is 9.4 amps, so 125% is 11.75 amps. The discharge valve of the pump is throttled back because wide open causes the motor to draw beyond its nameplate value. Thanks.


Tools for Electricians:

#102608 - 06/22/06 08:11 PM Re: motor overloads  
Rewired  Offline
Member
Joined: Jan 2006
Posts: 558
Hamilton, Ontario, Canada
I could be wrong but from what I have understood in the past the "service factor" is the percentage the motor can be overloaded for a SHORT DURATION without causing damage to the motor.. So really that motor will put out ( 10 * 1.15)= 11.5 horsepower ( 15% overload) for a short duration with no damage to the motor.. The overload heater being at 125% of nameplate FLA is just a MAXIMUM value of the setting of the overload heaters, not the percentage of how much you can overload the motor..

BTW, some overload heaters allow for the 125% rating.. you just size them to what your motor FLA is and thats it...should say somewhere on the overload or starter somewhere..

A.D


#102609 - 06/23/06 01:24 AM Re: motor overloads  
jay8  Offline
Member
Joined: Jul 2005
Posts: 183
Vancouver, BC
I pulled this definition from my old Cox's Electricians Guide to AC Motor Controls: service factor- the number by which the horsepower rating is multiplied to determine the maximum safe load that a motor may be expected to carry CONTINUOUSLY at its rated voltage and frequency."
Just curious if there any other thoughts out there.


#102610 - 06/26/06 06:50 PM Re: motor overloads  
Rewired  Offline
Member
Joined: Jan 2006
Posts: 558
Hamilton, Ontario, Canada
I picked up a handbook just now .. " IPT's electrical Handbook" and it says:

"Multiplying nameplate power by the service factor reflects how much the motor may be overloaded, PREFERABLY for brief periods"...
So I guess you could overload the motor continuously but it would shorten the life of the motor, as it is technically being run in an overloaded condition??!!

A.D



Member Spotlight
JoeKP
JoeKP
Berkley, MA
Posts: 144
Joined: March 2008
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.014s Queries: 14 (0.003s) Memory: 0.7592 MB (Peak: 0.8913 MB) Zlib enabled. Server Time: 2017-05-29 02:07:07 UTC