motor overloads #102607
06/22/06 12:34 PM
06/22/06 12:34 PM
J
jay8  Offline OP
Member
Joined: Jul 2005
Posts: 183
Vancouver, BC
I have a situation at work with a 10hp 600 volt motor driving a centrifugal pump. The 1.15 service factor of the motor allows us 125% for overload heater values, but can I continuously operate the motor at 125% of its nameplate value? In this case nameplate current is 9.4 amps, so 125% is 11.75 amps. The discharge valve of the pump is throttled back because wide open causes the motor to draw beyond its nameplate value. Thanks.

Tools for Electricians:
Re: motor overloads #102608
06/22/06 08:11 PM
06/22/06 08:11 PM
R
Rewired  Offline
Member
Joined: Jan 2006
Posts: 558
Hamilton, Ontario, Canada
I could be wrong but from what I have understood in the past the "service factor" is the percentage the motor can be overloaded for a SHORT DURATION without causing damage to the motor.. So really that motor will put out ( 10 * 1.15)= 11.5 horsepower ( 15% overload) for a short duration with no damage to the motor.. The overload heater being at 125% of nameplate FLA is just a MAXIMUM value of the setting of the overload heaters, not the percentage of how much you can overload the motor..

BTW, some overload heaters allow for the 125% rating.. you just size them to what your motor FLA is and thats it...should say somewhere on the overload or starter somewhere..

A.D

Re: motor overloads #102609
06/23/06 01:24 AM
06/23/06 01:24 AM
J
jay8  Offline OP
Member
Joined: Jul 2005
Posts: 183
Vancouver, BC
I pulled this definition from my old Cox's Electricians Guide to AC Motor Controls: service factor- the number by which the horsepower rating is multiplied to determine the maximum safe load that a motor may be expected to carry CONTINUOUSLY at its rated voltage and frequency."
Just curious if there any other thoughts out there.

Re: motor overloads #102610
06/26/06 06:50 PM
06/26/06 06:50 PM
R
Rewired  Offline
Member
Joined: Jan 2006
Posts: 558
Hamilton, Ontario, Canada
I picked up a handbook just now .. " IPT's electrical Handbook" and it says:

"Multiplying nameplate power by the service factor reflects how much the motor may be overloaded, PREFERABLY for brief periods"...
So I guess you could overload the motor continuously but it would shorten the life of the motor, as it is technically being run in an overloaded condition??!!

A.D


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
waymag
waymag
dallas, texas, USA
Posts: 68
Joined: January 2002
Show All Member Profiles 
Top Posters(30 Days)
Admin 13
Trumpy 11
sparky 7
Popular Topics(Views)
249,341 Are you busy
187,275 Re: Forum
176,630 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.022s Queries: 14 (0.004s) Memory: 0.9592 MB (Peak: 1.0910 MB) Zlib enabled. Server Time: 2018-09-21 14:04:09 UTC