516
17
I have a concrete box without means to connect a screw to it...It was installed in a block wall and the core is filled with concrete. It is for a GFI receptacle, no splices, wires in EMT go directly to the GFI, without claiming it is a Isolated grounding conductor...Is the EMT a good EGC for the metal box?
Thanks in advance, H2O
A properly made up EMT run is a grounding path. Did they also include a grounding conductor in the bundle coming in? If you really want a connection to the box and the installer wasn't polite enough to put a screw in the tapped hole you should be able to chip a little concrete out next to the box and use a clip. When I set the concrete boxes in my walls I ran a #10 screw a little longer than a typical "green ground screw" and put a dab of duct seal on the outside so I had a good void to install my ground screws.
Yes, I have a black/white/green with no way to bond box, other than the EMT right now. If I just feed the GFI with the conductors and have EMT to ground jbox, would that be code compliant or would I need to at the very least use a grounding clip?
Thanks again, H20
The box would be bonded via the EMT, however the presence of the green conductor would require that to be bonded to the box,
I would follow Greg and do the clip trick.
They also make "self grounding" GFCIs with the little brass tab on the yoke and a spring on the screw that I suppose would be legal.
I had the same thought on the self grounding, but that would be dependent on the device to box mounting.
ie: 4" sq raised cover. Some AHJs may not 'like' that.
We are supposed to trust that a properly made up metallic raceway grounds the box so this would be supplemental grounding but I do think the clip might be a better solution if it could be done in a non destructive way. I suppose a more elegant solution would be using a small diamond wheel in a rotary tool to eat out the concrete but most guys are not going to have that in their bag.