#99918 09/27/06 12:47 PM
Joined: Oct 2004
Posts: 132
M
Member
I believe the only listed for the purpose boxes can be found in the following links (warning, PDF's):
http://www.woodhead.com/data/current1488/multiple%20outlet%20boxes%20902.pdf http://www.woodhead.com/data/current3054/multitap%20902.pdf

I have seen FS boxes w/ kellem grips used as well, but I am not sure if they are listed for this.

Work Gear for Electricians and the Trades

Workgear for Electricians

#99919 09/27/06 02:05 PM
Joined: Jul 2004
Posts: 625
S
Member
The "threaded hub" in 314.23(H)(1) is only a suggestion, not a requirement. The requirement is that the conductors be protected against strain. If a connection to a KO accomplishes that, then it is also permitted.

As a note, I have never seen even one pendant around here that uses a box with a hub. I see four-square boxes all over the place.

#99920 09/27/06 04:40 PM
Joined: Jul 2004
Posts: 10,041
Likes: 37
G
Member
I doubt I would take a 4" square box hanging on a regular connector as a pendant. How do you keep the lock nut tight?
I'm sure there is a 110.3(B) in there somewhere if common sense isn't enough.


Greg Fretwell
#99921 09/27/06 05:23 PM
Joined: Oct 2004
Posts: 132
M
Member
Stamped steel boxes (4S, 5S, Handy Box, etc) w/ KO's are not for "portable" use. That means you can't make quadboxes, splitters, portable GFCI's etc out of them . The main reason for this is that the KO's bend inward and may touch the device screws, leading to problems. I believe their UL listing covers this...maybe somebody can post this?

#99922 09/27/06 08:08 PM
Joined: Dec 2000
Posts: 4,294
Member
Quote
the KO's bend inward
I've always wondered why they were called knockouts instead of knockins [Linked Image]
JBD,
My original Q dealt with fastened in place large machinery. I think it is addressed in Article 400. I'm not trying to look at one part of the NEC and not another. Sure I've got my opinion, but I'm trying to understand where I might be missing something. After all, that's what this forum's for.
336.10(7) doesn't seem to have anything to do with cord pendants.

#99923 09/28/06 06:59 PM
Joined: Apr 2002
Posts: 7,413
Likes: 9
Member
Electure:
I fail to see where in Art 400 you may find a good 'argument' to use cord to connect large machinery.

edit

I just re-read your opening post; OK, you said 'non-movable', so why not RMC/IMC?. Or, as you described it, why not lengthen the 'field installed..." to go 'up' to a suitable twistlock recept?? Or, RGC/IMC down to a suitable box; nipple to floor flange on floor, then a TL in the box?

The usual debate (EC to AHJ) 'physical damage'; the load on the OH crane could hit the RGC; (me) but it can't hit the cord??
9ec) 'vibration'; (me) OK, use sealtite for the final conn.

As I said above, been there, done it.

John

John

[This message has been edited by HotLine1 (edited 09-28-2006).]


John
#99924 09/29/06 05:02 PM
Joined: Jul 2001
Posts: 599
J
JBD Offline
Member
My point is that there are several places in the NEC that allow cords to fixed equipment.

400.7(A) only requires cord connectors for 3 of its 10 possible situations. So it is clear that cords can be used from one utilization device to another.

So another question is "what is a pendant", as it pertains to 400.7(A)(1)? Is it any vertical riser? We know plugs and receptacles are not required, because 400.7(B) does not apply to it.

Work Gear for Electricians and the Trades

Workgear for Electricians

#99925 10/02/06 08:45 PM
Joined: Apr 2002
Posts: 7,413
Likes: 9
Member
JBD:

You stated:
"My point is that there are several places in the NEC that allow cords to fixed equipment.
400.7(A) only requires cord connectors for 3 of its 10 possible situations. So it is clear that cords can be used from one utilization device to another.

So another question is "what is a pendant", as it pertains to 400.7(A)(1)? Is it any vertical riser? We know plugs and receptacles are not required, because 400.7(B) does not apply to it."

Your statement regarding 400.7 (A); I cannot understand what you mean!

There is no definition for "pendant" in Art. 100. I know of a 'pendant', as a control station, like for a rolling OH crane with various buttons or switches; in flex cord, into a strain relief connector.

There are probably 'pendant' receptacles, but, I have not seen any.

John


John
#99926 10/02/06 10:57 PM
Joined: Jul 2004
Posts: 10,041
Likes: 37
G
Member
Look at the fryer behind the counter at a burger king. Every one I have seen in SW Florida was supplied by an IEC309 connector from an SO cord pendant.


Greg Fretwell
#99927 10/03/06 09:43 AM
Joined: Jul 2001
Posts: 599
J
JBD Offline
Member
Is any vertical drop of flexible cable a pendant and therefore allowed by 400.7(A)(1)? Or, do pendants need to be "free hanging" and only fixed in place on one end?