NEC - Separation between control and power lines #99851
09/22/06 01:17 PM
09/22/06 01:17 PM
C
Currently  Offline OP
Member
Joined: Apr 2002
Posts: 53
TN
My book is at home now and I have this question for the industrial control people here.

Is there anything in the NEC that dictates a defined separation between control wiring and power wiring?

I.E. 14 inches per kilovolt ....

2017 / 2014 NEC & Related Books and Study Guides
Re: NEC - Separation between control and power lines #99852
09/22/06 03:09 PM
09/22/06 03:09 PM
E
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
so long as the wiring is separated by an enclosed wiring method, (NM cable, conduit, etc.) no.


Earl
Re: NEC - Separation between control and power lines #99853
09/26/06 12:38 PM
09/26/06 12:38 PM
J
jwhite  Offline
Member
Joined: Dec 2005
Posts: 64
Trenton, NC, USA
1/4 inch for class two and three. Or a suitable barrier.

Re: NEC - Separation between control and power lines #99854
09/26/06 01:14 PM
09/26/06 01:14 PM
G
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,493
Michigan USA
Need to know what the control wiring is controling. If it is Class 1 wiring and it is functionally associated with the power wiring there is no problem having it in the same raceway as long as the insulation on all the conductors has a high enough rating. If the control wiring is Class 2 then it can not be in the same raceway with the power wiring without a barrier. 725.26(B)(1), 725.55(A)


George Little

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
mxslick
mxslick
Atomic City, ID USA
Posts: 803
Joined: October 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 9
Albert 3
Popular Topics(Views)
254,005 Are you busy
190,401 Re: Forum
180,113 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.019s Queries: 14 (0.004s) Memory: 0.9613 MB (Peak: 1.0936 MB) Zlib enabled. Server Time: 2019-03-26 02:24:06 UTC