#99851 - 09/22/06 12:17 PM NEC - Separation between control and power lines  
Currently  Offline
Member
Joined: Apr 2002
Posts: 53
TN
My book is at home now and I have this question for the industrial control people here.

Is there anything in the NEC that dictates a defined separation between control wiring and power wiring?

I.E. 14 inches per kilovolt ....


2017 / 2014 NEC & Related Books and Study Guides

#99852 - 09/22/06 02:09 PM Re: NEC - Separation between control and power lines  
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
so long as the wiring is separated by an enclosed wiring method, (NM cable, conduit, etc.) no.


Earl

#99853 - 09/26/06 11:38 AM Re: NEC - Separation between control and power lines  
jwhite  Offline
Member
Joined: Dec 2005
Posts: 64
Trenton, NC, USA
1/4 inch for class two and three. Or a suitable barrier.


#99854 - 09/26/06 12:14 PM Re: NEC - Separation between control and power lines  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Need to know what the control wiring is controling. If it is Class 1 wiring and it is functionally associated with the power wiring there is no problem having it in the same raceway as long as the insulation on all the conductors has a high enough rating. If the control wiring is Class 2 then it can not be in the same raceway with the power wiring without a barrier. 725.26(B)(1), 725.55(A)


George Little


Member Spotlight
SafetyWired
SafetyWired
Pa, USA
Posts: 44
Joined: July 2013
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 14 (0.003s) Memory: 0.7604 MB (Peak: 0.8909 MB) Zlib enabled. Server Time: 2017-12-13 18:52:10 UTC