#99615 - 08/18/06 02:41 PM 517.13 Grounding of Receptacles in Patient Care Areas  
Takideezy  Offline
Junior Member
Joined: Aug 2006
Posts: 9
Williamsport,PA,USA
I am working on an Audiologist office, this is new construction. i believe that the patient examination area requires branch circuits to be wired per 517.13. Based on the installation requirements I plan to use Type AC cable that contains an insulated equipment grounding (bonding) conductor, marked as HFC- Health Care Facility Cable.

I'm stuck on the bonding requirements at the panel and the boxes where "hospital grade" receptacles will be installed on branch circuits. Is there a specific requirement for bonding to insure the redundant ground path is maintained? Are there specific cable clamps/connectors to be used with this cable?

Thanks for the help. Mike


2017 / 2014 NEC & Related Books and Study Guides

#99616 - 08/18/06 03:18 PM Re: 517.13 Grounding of Receptacles in Patient Care Areas  
raider1  Offline
Member
Joined: Jul 2005
Posts: 46
north logan, utah, US
Quote
Is there a specific requirement for bonding to insure the redundant ground path is maintained? Are there specific cable clamps/connectors to be used with this cable?


You must follow the manufactures listing requirments for termination of the cable. With that said most of the time you don't have to do anything with the bond wire but to cut it off or wrap it back over the cable sheath.

As for special connectors, all you need are connectors that are listed for use with AC cable.

Chris


#99617 - 08/18/06 03:58 PM Re: 517.13 Grounding of Receptacles in Patient Care Areas  
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Along with Chris's post, the insulated EGC is the only conductor that will attach to the box and the device, the same as any installation.

Are the HG devices being used for an engineers specification? If these rooms are just exam rooms they will not need HG devices as far as the NEC or NFPA 99 is concerned.

Roger


#99618 - 08/18/06 04:45 PM Re: 517.13 Grounding of Receptacles in Patient Care Areas  
Takideezy  Offline
Junior Member
Joined: Aug 2006
Posts: 9
Williamsport,PA,USA
It was my assumption that HG devices were required. However after re-reading 517.13B all it requires is that the grounding conductor be insulated and copper. I was likely also influenced by 517.16. Thanks Roger for the clarification. Anything else I'm missing?

Mike


#99619 - 08/18/06 08:53 PM Re: 517.13 Grounding of Receptacles in Patient Care Areas  
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Mike, I can't think of anything else at the moment.

BTW, welcome to the forum.

Roger


#99620 - 08/18/06 09:52 PM Re: 517.13 Grounding of Receptacles in Patient Care Areas  
Takideezy  Offline
Junior Member
Joined: Aug 2006
Posts: 9
Williamsport,PA,USA
Thanks Roger - It's a great forum. I have been lurking for a while. Mike



Member Spotlight
mxslick
mxslick
Atomic City, ID USA
Posts: 803
Joined: October 2004
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.016s Queries: 14 (0.002s) Memory: 0.7774 MB (Peak: 0.9221 MB) Zlib enabled. Server Time: 2017-10-18 18:28:59 UTC