When a Fire pumps Fed from Mulitple sources (Generator- Power Company) the way I read it both sources are required to comply with 695.6 (B) 1 or 2 or 3 . Any input on this Please. Both Generator and Power company sources are remote from Fire Pump control transfer switch & controller.

Work Gear for Electricians and the Trades

Workgear for Electricians

#99557 08/14/06 09:06 PM
Joined: Jan 2004
Posts: 1,507
G
Member
Ernie- I'm far from being the Firepump Guru on this Board but there aren't any exceptions that I read so my answer is yes both supplies must comp[y with 695.6(B) 1 or 2 or 3.

Hey ask easier questions like "What color is a green ground screw?"

See Ya in TC


George Little