liquidtight #99512
05/26/06 11:59 PM
05/26/06 11:59 PM
V
victor  Offline OP
Junior Member
Joined: May 2006
Posts: 3
Las Vegas
Hi I would like to know where in the NEC talks about using liquidtight conduit to connect a dry type transformer because fo vibration. Thank you

2017 / 2014 NEC & Related Books and Study Guides
Re: liquidtight #99513
05/27/06 06:41 AM
05/27/06 06:41 AM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Welcome to the forum victor.

You will not find anything in the NEC requiring liquidtight conduit to be used to connect a dry type transformer because of vibration.

It is just a design choice buy the installer.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: liquidtight #99514
05/27/06 02:03 PM
05/27/06 02:03 PM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
I'll go a bit farther...

True, the NEC does not address the matter. However, NECA standards document the use of flex at transformers as "trade practice", or good workmanship.

That aside, I noticed recently that some transformers have internal rubber mounts, so the piping actually does not connect to the part that vibrates.

I still like to see flex at the case, though. Old habits die hard.

Re: liquidtight #99515
05/30/06 09:40 PM
05/30/06 09:40 PM
V
victor  Offline OP
Junior Member
Joined: May 2006
Posts: 3
Las Vegas
hi thank you for your reply, where can I get a copy of NECA stating the use of liquid flex as a good workmanship. Thank you


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
BEAMEUP
BEAMEUP
WA
Posts: 27
Joined: December 2004
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
252,150 Are you busy
189,154 Re: Forum
178,825 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.016s Queries: 14 (0.003s) Memory: 0.9591 MB (Peak: 1.0905 MB) Zlib enabled. Server Time: 2018-12-11 20:20:36 UTC