ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
110.26
by gfretwell. 02/18/18 12:14 AM
2018 Code Explained
by Potseal. 02/14/18 03:16 PM
Air Compressor feeder conductor sizing
by Potseal. 02/14/18 03:11 PM
New in the Gallery:
Housebilding DIY wiring
SE cable question
Who's Online Now
0 registered members (), 11 guests, and 10 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Drainage basin #99485
01/17/06 09:31 PM
01/17/06 09:31 PM
H
harold endean  Offline OP
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
I am looking at a job that will be going down in a few weeks. The engineer wants to run the main service entrance pipes underground and right through a major drainage catch basin between 2 buildings. Is there anything in the code that says it could or could not be allowed? In the 2002 NEC or the 2005 NEC? I am already starting to have problems with a too small electrical room. We shall have to go head to head on some of these issues. Thank you.

2017 / 2014 NEC & Related Books and Study Guides
Re: Drainage basin #99486
01/17/06 10:04 PM
01/17/06 10:04 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,180
Estero,Fl,usa
Once something is "wet location" I don't think it can be wetter. (a "double secret wet location"?)
You should think of physical damage problems which become very serious when it is a service lateral.
Can they put it at the bottom and cover it with concrete?


Greg Fretwell
Re: Drainage basin #99487
01/20/06 09:09 PM
01/20/06 09:09 PM
H
harold endean  Offline OP
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
Greg,

Those were several issues I had with this application. The "Wet" location and the damage that can be done if they ever decide to dredge out the area or dig it deeper. I guess I can make them encase the service laterals in concrete. The main reason is that if the pipes leak, they could flood out a CT cabinet. I have seen this happen before. The bottom fell out of a CT cabinet due to water damage.

Re: Drainage basin #99488
01/20/06 10:34 PM
01/20/06 10:34 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,180
Estero,Fl,usa
Underground pipes are expected to have water in them, Arranging your equipment to keep the water out is another issue. I do see your point though, if your CT can is lower than the expected "high tide" in the catch basin. All the more a reason to bury them in concrete or just stay out of the basin. You could be expected to deal with a little condensation but you shouldn't have to worry about draining the whole street through your equipment if you had a "rust through".


Greg Fretwell
Re: Drainage basin #99489
01/22/06 10:44 AM
01/22/06 10:44 AM
H
harold endean  Offline OP
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
Greg,

I guess I could also ask for a letter from the EE stating that in his opinion, it is safe to install it this way. That way in case something does go wrong, I can have it on record that he could be responsable for it.

Re: Drainage basin #99490
01/23/06 12:39 AM
01/23/06 12:39 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,180
Estero,Fl,usa
Make sure he understands and addresses all of your concerns. The engineer may not have thought of all the bad things you have seen in your career.
He may think nobody ever digs and conduit lasts forever. Maybe he needs to see a catastrophic failure of a service conductor.
At a certain point you are still the AHJ and the buck stops on your desk. As my boss used to tell me when I was inspecting "make it safe".


Greg Fretwell

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
RH1
RH1
California
Posts: 22
Joined: August 2009
Show All Member Profiles 
Top Posters(30 Days)
Admin 8
Popular Topics(Views)
244,037 Are you busy
181,031 Re: Forum
171,277 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.015s Queries: 14 (0.003s) Memory: 0.9756 MB (Peak: 1.1227 MB) Zlib enabled. Server Time: 2018-02-21 15:04:42 UTC