markp Offline OP
Has anyone noticed the subtle deletion of "severe" from 250.64? The way I read it now, you need to protect GEC's sized 4 and larger from physical damage whereas previously it only had to be protected from severe physical damage. We may end up needing to put just about every GEC in conduit...
[This message has been edited by markp (edited 09-07-2005).]
Mark
Kent, WA
Workgear for Electricians
#99443 09/07/05 06:38 PM
Thats a great catch! Nicely done!
Ryan Jackson,
Salt Lake City
#99444 09/07/05 10:15 PM
"Exposed to physical damage" is always going to be a judgement call. This change has certainly tossed some mud in the water. Basically if you can't run the #4 without a raceway, you can't run it is PVC either because that says 352.10(F) Exposed. For exposed work where not subject to physical damage if identified for such use"
#99445 11/04/05 02:05 PM
And yet 250-64(b) seems to imply that a #6 or smaller can be protected with PVC if exposed to physical damage.
#99446 11/04/05 04:13 PM
Someone explain to me how a GEC Indoors, behind a transformer, going up a wall, would be exposed to physical damage?
Or for that matter, how does a GEC originating in a panel, going up to building steel, get damaged?
Dnk...
#99447 11/04/05 05:57 PM
Dnk, I think we all agree there are places where a wiring method is not subject to any physical damage. This question pertains to the difference between severe physical damage and <some other kind of> physical damage.
This is just going to be a judgement call.
#99448 11/04/05 06:16 PM
I know G, just curious if any one has seen this happen and how.
I can't imagine how a GEC can be damaged, other than blatant negligence.
Dnk...
#99449 11/04/05 07:02 PM
Usually GECs get damaged by lawn mowers or other equipment running up next to the wall from what I see. I can't see a problem inside a building unless it is a shop or warehouse where there is some heavy material being stored against or moving by an unprotected run.
#99450 11/06/05 02:24 AM
Does GEC stand for grounding equipment conductor? I am used to seing as EGC. I guess its probably which coast you live on.
#99451 11/06/05 03:48 AM
GEC = Grounding electrode conductor
EGC = Equipment grounding conductor
GEC is for connecting your grounding electrodes together to form your grounding electrode system.
EGC is the wire/conduit to bond equipment.
[This message has been edited by dmattox (edited 11-06-2005).]