This isn't new to 05 but here's the question: As we read this it disallows a paralleled feeder to a sub panel (from a main dist panel) if the sets are in 2 or 3 pipes (one set per pipe). We have many panels fed by two EMT pipes that originate at a breaker in a dist panel, where each contains all the phases, a neutral and a grond. We're obviously missing something here. Maybe we aren't defining "common neutral" properly. Or maybe we have a lot of illegal panels. Your input is appreciated.
|
|
|
|
Joined: Jul 2004
Posts: 9,931 Likes: 34
Member
|
The reference to common neutral means you are only running one neutral back to the panel for multiple parallel phase sets. If you pull a neutral with each set you can split them up in separate raceways. It is just an inductive heating problem because all neutral current would be in one pipe with the outgoing current split up among the others.
Greg Fretwell
|
|
|
|
Joined: Aug 2001
Posts: 335
OP
Member
|
We follow that but here's what threw us: look at the cut & paste from the code ... what does the NEC mean by "ALL conductors of ALL feeders". Doesn't that seem to indicate every individual conductor of each set? Or do they interpret each set as a separate feeder? Or, again, are we just interpreting it wrong?
"Where installed in a metal raceway or other metal enclosure, all conductors of all feeders using a common neutral shall be enclosed within the same raceway or other enclosure as required in 300.20."
|
|
|
|
Joined: Nov 2000
Posts: 2,148
Member
|
Steve, If you have a grounded conductor in each raceway, you don't have a common neutral and the section that you cited does not apply. The section for your installation is 310.4. Don
Don(resqcapt19)
|
|
|
|
Joined: Aug 2001
Posts: 335
OP
Member
|
I see we were just interpereting "common neutral" wrong. Thanks for the input.
|
|
|