ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
VDE 0100 to introduce AFCIs
by sparky. 01/20/18 05:09 PM
MRI LED lights dimmer control replacement - wow!
by Potseal. 01/19/18 08:52 PM
Video: Inventor of the GFCI self-testing shocks
by Bill Addiss. 01/17/18 11:11 PM
FPE in Germany
by HotLine1. 01/17/18 07:07 PM
Fujifilm Recalls Power Adapter Wall Plugs
by Admin. 01/16/18 07:04 PM
New in the Gallery:
Housebilding DIY wiring
SE cable question
Who's Online Now
1 registered members (HotLine1), 13 guests, and 13 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
215.4B #99425
11/02/05 09:05 PM
11/02/05 09:05 PM
S
Steve Miller  Offline OP
Member
Joined: Aug 2001
Posts: 325
Loudoun Cty, VA
This isn't new to 05 but here's the question:
As we read this it disallows a paralleled feeder to a sub panel (from a main dist panel) if the sets are in 2 or 3 pipes (one set per pipe). We have many panels fed by two EMT pipes that originate at a breaker in a dist panel, where each contains all the phases, a neutral and a grond. We're obviously missing something here. Maybe we aren't defining "common neutral" properly. Or maybe we have a lot of illegal panels.
Your input is appreciated.

2017 / 2014 NEC & Related Books and Study Guides
Re: 215.4B #99426
11/02/05 11:45 PM
11/02/05 11:45 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,166
Estero,Fl,usa
The reference to common neutral means you are only running one neutral back to the panel for multiple parallel phase sets. If you pull a neutral with each set you can split them up in separate raceways.
It is just an inductive heating problem because all neutral current would be in one pipe with the outgoing current split up among the others.


Greg Fretwell
Re: 215.4B #99427
11/03/05 06:22 AM
11/03/05 06:22 AM
S
Steve Miller  Offline OP
Member
Joined: Aug 2001
Posts: 325
Loudoun Cty, VA
We follow that but here's what threw us: look at the cut & paste from the code ... what does the NEC mean by "ALL conductors of ALL feeders". Doesn't that seem to indicate every individual conductor of each set? Or do they interpret each set as a separate feeder? Or, again, are we just interpreting it wrong?

"Where installed in a metal raceway or other metal enclosure, all conductors of all feeders using a common neutral shall be enclosed within the same raceway or other enclosure as required in 300.20."

Re: 215.4B #99428
11/03/05 07:27 AM
11/03/05 07:27 AM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Steve,
If you have a grounded conductor in each raceway, you don't have a common neutral and the section that you cited does not apply. The section for your installation is 310.4.
Don


Don(resqcapt19)
Re: 215.4B #99429
11/03/05 05:51 PM
11/03/05 05:51 PM
S
Steve Miller  Offline OP
Member
Joined: Aug 2001
Posts: 325
Loudoun Cty, VA
I see we were just interpereting "common neutral" wrong. Thanks for the input.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Potseal
Potseal
Saskatchewan
Posts: 259
Joined: February 2013
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 16
Potseal 15
Popular Topics(Views)
243,571 Are you busy
180,369 Re: Forum
170,845 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.013s Queries: 14 (0.003s) Memory: 0.9675 MB (Peak: 1.1059 MB) Zlib enabled. Server Time: 2018-01-21 00:54:27 UTC