ground loops #98873
06/20/06 05:12 PM
06/20/06 05:12 PM
S
Steve T  Offline OP
Member
Joined: Feb 2001
Posts: 306
Oak Park, IL, USA
I had an engineer tell me today that a tankless hot water heater with sensitive electronic controls was not operating properly because a 'second ground' run thru a correctly installed emt was connected directly to the neutral bus in the service panel and not to a separate ground bus. He understands the two busses connect directly to one another in the panel, but he says it makes a difference and can create a ground loop which affects the point of reference of the electronic controls at the unit.

Could a foot and a half of #4 really make a difference? Maybe this should be in the technical area, but I was having trouble getting that one up.

2017 / 2014 NEC & Related Books and Study Guides
Re: ground loops #98874
06/20/06 05:19 PM
06/20/06 05:19 PM
G
gfretwell  Online Content

Member
Joined: Jul 2004
Posts: 9,300
Estero,Fl,usa
Sounds pretty shaky to me


Greg Fretwell
Re: ground loops #98875
06/20/06 05:35 PM
06/20/06 05:35 PM
L
LarryC  Offline
Member
Joined: Jul 2004
Posts: 783
Winchester, NH, US
Is there a significant amount of current running thru this 'second ground' wire? If so, is the temperature sensor wiring wrapped around this current carrying wire?

LarryC

Re: ground loops #98876
06/20/06 06:30 PM
06/20/06 06:30 PM
L
Larry Fine  Offline
Member
Joined: Feb 2005
Posts: 693
Richmond, VA
Sounds like a shipment of male bovine excrement to me.


Larry Fine
Fine Electric Co.
fineelectricco.com
Re: ground loops #98877
06/20/06 07:10 PM
06/20/06 07:10 PM
L
Larry Fine  Offline
Member
Joined: Feb 2005
Posts: 693
Richmond, VA
To add: I'd be willing to move the redundant ground to the other bus just to shut him up (meaning call his bluff).


Larry Fine
Fine Electric Co.
fineelectricco.com
Re: ground loops #98878
06/20/06 08:58 PM
06/20/06 08:58 PM
G
gfretwell  Online Content

Member
Joined: Jul 2004
Posts: 9,300
Estero,Fl,usa
If there is a ground loop it is in his equipment not your wiring. There should be no way a "ground loop" in the line side of any equipment should affect the "data" side. He may have something grounded that shouldn't be but it is not in an article 300 wiring method. It is in his LAN or internal wiring.


Greg Fretwell
Re: ground loops #98879
06/20/06 09:27 PM
06/20/06 09:27 PM
S
Steve T  Offline OP
Member
Joined: Feb 2001
Posts: 306
Oak Park, IL, USA
Thanks. I tend to agree with you guys, but this guy says their company does a lot of engineering for sensitive equipment--Honeywell and some others-- and says somethings dealing with inductance, capacitance (unspecific) he may not have known exactly, can cause this situation. When they removed the second ground all together, the unit works fine.

Like I said, I don't see how a short piece of wire can change all of this (especially when it is a #4 in a 200amp panel or a direct connection thru the panel enclosure itself) I guess I'd need to see the technical specs.

He said they were measuring a 1/2 amp on the ground wire. I don't know how they know there isn't current on the conduit.

Where's Scott? He usually has a complex answer.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Niko
Niko
Campbell, CA
Posts: 356
Joined: August 2006
Show All Member Profiles 
Top Posters(30 Days)
sparky 11
Admin 7
Popular Topics(Views)
250,699 Are you busy
188,161 Re: Forum
177,857 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.023s Queries: 14 (0.004s) Memory: 0.9851 MB (Peak: 1.1368 MB) Zlib enabled. Server Time: 2018-10-24 05:26:24 UTC