ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Recent Posts
VFD MotorFeeders
by gfretwell. 10/19/17 01:02 AM
Generator Cable Sizing
by brsele. 10/18/17 07:39 PM
What do you do?
by gfretwell. 10/17/17 01:08 AM
Good ol' copper pipe in the fuse holder trick
by HotLine1. 10/16/17 07:16 PM
Another generator question
by HotLine1. 10/16/17 07:02 PM
New in the Gallery:
Gallery Test
Popular Topics(Views)
241,388 Are you busy
177,345 Re: Forum
168,958 Need opinion
Who's Online Now
0 registered members (), 37 guests, and 7 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#98810 - 06/08/06 09:43 AM NEC 450.4(A) & Autotransformer overcurrent protection  
SteveFehr  Offline
Member
Joined: Mar 2005
Posts: 1,213
Chesapeake, VA
NEC 2005, Article 450.4(A) has a confusing clause regarding autotransformer overcurrent protection:

An overcurrent device shall not be installed in series with the shunt winding (the winding common to both the input and the output circuits) of the autotransformer between Points A and B [Output taps] as shown in Figure 450.4.

What, exactly, do they mean by this? It sounds almost as though they're probihiting overcurrent protection on the output, but that makes no sense and this is directly contradicted by the table referenced earlier in the paragraph. Do people actually physically open up these transformers to break the windings so they can put a breaker in the middle, is that what they're prohibiting?


2017 / 2014 NEC & Related Books and Study Guides

#98811 - 06/08/06 11:18 PM Re: NEC 450.4(A) & Autotransformer overcurrent protection  
winnie  Offline
Member
Joined: Sep 2003
Posts: 649
boston, ma
Yup, they are prohibiting an overcurrent device in the middle. If such an overcurrent device were to operate, then the output voltage would rise to the input voltage.

Since the current rating of the shunt winding is less than that of the transformer and the series winding, I can see why someone might want to put an overcurrent device in that location. This would be a case of a safety improvement in a component of a system reducing the over-all safety of the system.

-Jon


#98812 - 06/09/06 01:54 PM Re: NEC 450.4(A) & Autotransformer overcurrent protection  
Larry Fine  Offline
Member
Joined: Feb 2005
Posts: 693
Richmond, VA
Steve, I doubt they're concerned with someone opening the transformer to insert a breaker. Referring to the diagram again, I believe they don't want a breaker between the bottom of the winding and point B; t should be in the line to the left of point B.


Larry Fine
Fine Electric Co.
fineelectricco.com


Member Spotlight
noderaser
noderaser
Portland, Oregon, United States
Posts: 404
Joined: March 2007
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.013s Queries: 14 (0.003s) Memory: 0.7534 MB (Peak: 0.8752 MB) Zlib enabled. Server Time: 2017-10-19 10:41:55 UTC