ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
sparky 5
Recent Posts
Holiday Wishes to all!!
by HotLine1. 12/15/17 07:20 PM
Dimmable LED 2x4 lay in fixtures
by HotLine1. 12/15/17 07:15 PM
2017 NEC Changes
by HotLine1. 12/15/17 07:06 PM
Casino Wiring methods
by HotLine1. 12/09/17 10:44 AM
Ground wire Size to water Line.
by HotLine1. 12/05/17 12:11 PM
New in the Gallery:
Gallery Test
Popular Topics(Views)
243,084 Are you busy
179,524 Re: Forum
170,439 Need opinion
Who's Online Now
0 registered members (), 7 guests, and 11 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#98780 - 06/06/06 04:45 PM HVAC conductor sizing  
Gee  Offline
Junior Member
Joined: Oct 2005
Posts: 9
baton rouge LA, USA
Hey guys, a question:

I have a 480v, 3 phase rooftop unit that we installed #10 conductors as per plans.
Now the units arrived and has a Min.Circuit Ampacity of 30.2 amps.
Is the #10 conductor acceptable using 310-16 value of 35 amps ?
If this is acceptable, only if the OCP is sized at 35 amps ?
I am fairly certain that even if these are acceptable, I still will be required to change the disconnect to a 60 amp unit w/ 35 amp fuses.

Thanks in advance


2017 / 2014 NEC & Related Books and Study Guides

#98781 - 06/06/06 05:06 PM Re: HVAC conductor sizing  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,883
Brick, NJ USA
OK, what's the data on the AC nameplate?
Min circ amps? (30.2)
Max OCP??

Unit nameplate data governs the MOCP.

Yes, IF you need 35 amp fuses, then a 60 amp FD is req.

Refer to the "*" under 310.16 to go to 240.4

As to the 'plans', time to request a change order and pull in #8 & change the disco.

John


John

#98782 - 06/06/06 05:19 PM Re: HVAC conductor sizing  
caselec  Offline
Member
Joined: Apr 2002
Posts: 558
San Jose, CA
John, why do the #10’s need to be replaced with #8’s? As long as the MCA is 35 amps or less #10 THWN is acceptable for this installation.

Curt


Curt Swartz

#98783 - 06/06/06 05:25 PM Re: HVAC conductor sizing  
Gee  Offline
Junior Member
Joined: Oct 2005
Posts: 9
baton rouge LA, USA
Min cir- 30.2
Max fuse - 35
I am sure I have to checge the disconnect. But can I get by with the 35 amp allowance for #10 for HVAC loads.
Does *240.4(D)> 240.4(G)table ( Air-condition refrigeration) > 440,part VI allow the # 10 to be protected at 35 amps ?
I am confused to say the least.
Seems like one day after 20 years I maybe can actually fuse # 10 at 35 amps as per 310-16. If not why do they even list 35 amps for #10


#98784 - 06/06/06 06:12 PM Re: HVAC conductor sizing  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
#10 wire is fine and 240.4(G) allows protection per Article 440. I suspect that he/she might end up with an protection larger than 35a. based on what the nameplate of the AC says. This larger protector is not really overload protection for the wire but merely short circuit and ground fault protection. It no doubt will be a 60a. switch unless he is using a breaker. The actual overload protection is internal in the AC and in an overload situation this would permit the branch circuit conductors from being damaged.
Just as a side note, the horsepower rating of a 30a. switch would not be adaquate for this large an AC.

[This message has been edited by George Little (edited 06-06-2006).]


George Little

#98785 - 06/06/06 06:37 PM Re: HVAC conductor sizing  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,883
Brick, NJ USA
Gee:
Sorry, but YES you can use #10 per 440.
20 years and you get to do it! (440)
I just didn't go to 440.
Don't forget the Change Order for the 60 amp FD

Curt:
Yes, #10 is OK by NEC.

George:
Based on Gee's response nameplate is 35 A MOCP, and he said "fuse".

However, and this is OPINION, not NEC:
Consideration has to be given to length of circuit conductors, ambient temp of circuit (on roof, in bar joists, etc) for conductor sizing. None of this was asked by GEE, nor asked by me in my reply. I would do this install with minimum #8, possibly #6.

John


John


Member Spotlight
akmaster
akmaster
alaska
Posts: 70
Joined: June 2012
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.017s Queries: 14 (0.003s) Memory: 0.7779 MB (Peak: 0.9235 MB) Zlib enabled. Server Time: 2017-12-17 07:57:37 UTC