#98650 11/08/04 07:48 PM
Joined: Aug 2003
Posts: 1,374
R
Ryan_J Offline OP
Moderator
New section 250.104(D) seems a bit strange to me, but perhaps I am reading it wrong. The way I am reading it, it would be required to bond the closest metal water piping even if I am using the structural metal as the electrode. Likewise, if I am using the water pipe as my electrode, I have to bond the nearest structural metal. Does this seem strange to any one else? I mean, 250.50 already requires them to be bonded together, why the redundancy?


Ryan Jackson,
Salt Lake City
Work Gear for Electricians and the Trades

Workgear for Electricians

Joined: Jan 2003
Posts: 4,391
I
Moderator
It sounds very much like 2002 250.104(A)(4)


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Joined: Aug 2003
Posts: 1,374
R
Ryan_J Offline OP
Moderator
Interesting...I never even noticed that before shocked


Ryan Jackson,
Salt Lake City
Joined: Jun 2003
Posts: 681
P
Member
Ryan
My understanding of this requirement is to keep the potential of the different systems in the area of the SDS as close to 0 as possible.