Article 110.9 #98557
06/01/06 06:10 PM
06/01/06 06:10 PM
S
ShockMe77  Offline OP
Member
Joined: Jun 2005
Posts: 821
Rahway, New Jersey
I had an inspector question me about the interupt rating on a 200 amp main breaker today on a job I am finishing that another electrician started. Yes, it is a pain in the neck finishing somone elses work.

Anyway, I have a 300 amp underground feed to the meter pan, and 2 raceways out to a pair of 200 amp main breaker panels. The interupt rating on the MB is 22,000.

Is this sufficient?

Remember, I did not install the service, nor do I know enough about the formula for figuring the interupt rating. I have to assume that the rating is based on the largest ungrounded conducter from the POCO.

The AHJ also noted that he would prefer that I also strip back the insulation on all of my GEC's where they enter the panel for heat protection. Is he serious?

2017 / 2014 NEC & Related Books and Study Guides
Re: Article 110.9 #98558
06/01/06 07:50 PM
06/01/06 07:50 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,963
Brick, NJ USA
Shock:
AIC (fault current) is available from PSE&G. Resi should be 'fine' with a 22K breaker. Most areas are 10K, a few are 15K.

Calculation requires impedance of transformer, length/size of drop, length/size of your service conductors, for starters. "Bussman" has a fairly simple point-to-point method that works; but you have to like numbers.

I'm working on preparing a AIC course, hopefully I'll have it ready by fall/winter.

If you want further info, send me an e-mail, and I can get you the literature.

As to the 'stripped ground conductors & heat???? What Article did he cite??

John


John
Re: Article 110.9 #98559
06/02/06 08:59 AM
06/02/06 08:59 AM
R
Ryan_J  Offline
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
I have talked to some different people that I know throughout the country on this, and the consensus is that most power companies won't provide more than 10K available to dwellings, unless the dwelling unit is quite large.


Ryan Jackson,
Salt Lake City
Re: Article 110.9 #98560
06/02/06 09:38 AM
06/02/06 09:38 AM
J
JBD  Offline
Member
Joined: Jul 2001
Posts: 599
WI, USA
The major POCOs, in Wisconsin have required 22K AIC rated equipment for almost 20 years now. They typically feed (4) houses from a single padmount, so they could easily exceed the 10K fault level if they buy 2%Z transformers or put in an oversized one. This is one reason they give such high "design" fault values, to prevent future problems as they upgrade their equipment.

If you need 22K rated equipment make sure the branch circuits are either fully or series rated also. Do not just look at the AIC rating of the main.

What type of heat is he expecting on the GEC?

Re: Article 110.9 #98561
06/02/06 05:40 PM
06/02/06 05:40 PM
S
ShockMe77  Offline OP
Member
Joined: Jun 2005
Posts: 821
Rahway, New Jersey
Thanks for all the replies. I never had an inspector ask me about interupt ratings for a residential service before. Thought it was a bit strange. I understand these issues become much more important when working with higher voltages so I thought I'd take the time to try and find out more.

The AHJ didn't cite any code referrence for stripping back the GEC at the enclosure. I sure as heck don't see one, that's for sure. Is the AHJ out of line for requesting this to be done in order to get a final? AND the service has already been inspected, and passed, but additional work has been done (finished bsmt) since the original inspection.

Re: Article 110.9 #98562
06/02/06 06:48 PM
06/02/06 06:48 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,963
Brick, NJ USA
Ryan:
Some areas here in NJ have resi 'areas' that PSE&G specs "high" AIC with the occasional 22K in mixed use neighborhoods.

JBD:
I'll offer a guess, at least 70% of resi in No. & Central is overhead, pots on poles. Newer neighborhoods are BUD.

Shock:
I'm sending you an e-mail for further info on the GEC 'heat' thing; I'm curious!!

John


John

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Top Posters(30 Days)
twh 12
Popular Topics(Views)
246,837 Are you busy
184,197 Re: Forum
173,440 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.024s Queries: 14 (0.004s) Memory: 0.9770 MB (Peak: 1.1177 MB) Zlib enabled. Server Time: 2018-05-20 09:48:18 UTC