Can someone explain to me the change to 210.12 Arc Fault Circuit-Interrupter Protection, "require that all dwelling unit bedroom branch circuit AFCI protection devices must be listed as a "combination Type AFCI", effective Jan. 1 2008." First of all I have never heard of the "combination type AFCI, and secondly the way I understand it is all 120V branch circuits being supplying 15 or 20A outlets in bedrooms must be AFCI protected. Does that include the lighting outlets, fan outlets, and recepticle outlets? Need clarification please..
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
The two biggest differences between the AFCI's is that the combination type is supposed to trip at 5 miliamps of current as opposed to 75, and the combination type is also supposed to detect arc faults after the outlet, such as cord and plug connected equipment.
As for your other questions, yes, all outlets in the bedroom (120 volt, 15/20 amp) are to be protected. This includes receptacles, light fixtures, smoke detectors, etc...
Ryan Jackson, Salt Lake City
|
|
|
|
Joined: Nov 2000
Posts: 2,148
Member
|
Ryan, I believe that it is 5 amps, not 5mA for the combination AFCI. Don
Don(resqcapt19)
|
|
|
|
Joined: Dec 2002
Posts: 18
OP
Member
|
If it is all outlets does that mean the smoke detectors and ceiling fans because ceiling fans tend to trip the AFCI.
|
|
|
|
Joined: Jan 2004
Posts: 1,507
Member
|
I was under the impression that the "combination" was for series and parallel arcs. since the current (no pun intended) ones only protect from parallel arcs.
George Little
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
Good catch Don, thanks. 5 amps indeed, not 5 miliamps (thank heavens).
Ryan Jackson, Salt Lake City
|
|
|
|
Joined: Apr 2004
Posts: 201
Member
|
George, you are correct. - - - - - - - - - - - - - - - - - - - - - - - - - - - Charlie Eldridge, Indianapolis, Utility Power Guy
Charlie Eldridge, Indianapolis Utility Power Guy
|
|
|
Posts: 201
Joined: April 2004
|
|
|
|