#98501 12/30/04 08:52 PM
Joined: Dec 2004
Posts: 46
T
ToHo Offline OP
Member
Hi... Just wanted some feed back on installing 2 ground rods for a residential service instead of 1 ground rod and the water main. Speaking with a inspector here in Rochester NY , he said they would prefer to see 2 ground rods. That was new to me.. anybody have a opinion on this subject... thanks ToHo

Horizontal Ad
#98502 12/30/04 09:20 PM
Joined: Apr 2004
Posts: 201
Member
Please read 250.50. It requires the water piping system to be used as a grounding electrode (assuming it is in contact with the earth for 10 ft or more) and another grounding electrode. If the additional grounding electrode is a driven electrode, a maximum of 25 ohms must be met or a second one must be driven no closer than 6 ft to the first one. [Linked Image]

- - - - - - - - - - - - - - - - - - - - - - - - - - -
Charlie Eldridge, Indianapolis, Utility Power Guy


Charlie Eldridge, Indianapolis Utility Power Guy
#98503 12/30/04 09:59 PM
Joined: Dec 2004
Posts: 46
T
ToHo Offline OP
Member
Thanks charlie... I agree 100%. Its always nice to get another view. If a well is used on the premise w/ pvc piping into the house. Would you use 2 ground rods or could you use only one if the ohms reading was acceptable?

#98504 12/31/04 12:42 AM
Joined: Dec 2004
Posts: 12
G
Member
You would be compliant with only one rod as long as the resistance is less than 25 ohms. Also, even though the waterpipe from the well is PVC, if the water system in the house is metallic, then it must still be bonded to the service. Not as an electrode, but to make it the same potential as the equipment grounds.

#98505 12/31/04 08:53 AM
Joined: Apr 2004
Posts: 201
Member
Gary, I agree completely. [Linked Image]


Charlie Eldridge, Indianapolis Utility Power Guy

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
Posts: 165
Joined: March 2007
Top Posters(30 Days)
dsk 1
Popular Topics(Views)
337,581 Are you busy
262,941 Re: Forum
243,222 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5