#9835 05/16/02 09:12 AM
Joined: Mar 2001
Posts: 2,056
R
Member
I believe that literally speaking, it violates 200.6(A). The "colored tracer threads in the braid" statement doesn't apply here.
200.6(D) seems explicit in it's intent.

That being said, I think this stuff will probably be approved in many residential applications.

Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

#9836 05/16/02 09:36 AM
Joined: Feb 2002
Posts: 840
C
Member
'66-

Wire is quite cheap right now, and it has been for the past few years. $.08 a foot sounds similar to prices around here (new england). Enjoy these prices while they last!


Code issues aside, this new cable is also great for electricians who don't like using multiwire circuits.


Peter
#9837 05/16/02 10:32 AM
Joined: Nov 2000
Posts: 2,148
R
Member
Redsy,
I agree that it has a good use and will most likely be accepted by the AHJ, but it is a code violation. Maybe we'll see proposals from Southwire for a 2005 change.
Don(resqcapt19)


Don(resqcapt19)
#9838 05/19/02 10:49 AM
Joined: Nov 2000
Posts: 2,236
Likes: 1
Member
What about ampacity derating for cables with more than 3 current carrying conductors?

Assuming 20 Amp required for each kitchen circuit, seems it would have to be #10 to be Kosher...


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
#9839 05/19/02 11:50 AM
Joined: Nov 2001
Posts: 280
M
Member
'66
Thats a good question, if the neutrals are considered current carrying conductors then we would have to derate 80 %, Right ?
But for derating purposes can we not use the table 310.16 which gives No.12 at 25 amps and the 80 % would be 20 amps???


-Mark-

#9840 05/19/02 01:37 PM
Joined: Apr 2002
Posts: 558
C
Member
Actually 334.80 says you can use the 90C column for derating purposes. #12 = 30 amps X 80% = 24 amps, well over the 20 amps permitted.


Curt Swartz
#9841 05/19/02 03:11 PM
Joined: Nov 2000
Posts: 2,236
Likes: 1
Member
Ampacity derating is something I don't quite fully comprehend...

It is so ignored here, that and conduit and box fill...

The more I learn, the more I realize what I don't know...

And there's unlicenced people out here "doing folks a favor" and they think they know enough.

Go figure...

[Linked Image]


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

#9842 05/19/02 03:47 PM
Joined: Apr 2001
Posts: 449
F
Member
The 4 conductor NM will also be handy for wiring those bath heat-vent-light units.

#9843 05/19/02 05:29 PM
Joined: Oct 2000
Posts: 5,393
S
Member
Fred,
you may be onto something there....

#9844 05/19/02 06:18 PM
Joined: Apr 2002
Posts: 2,527
B
Moderator
On the 4-wire romex, don't forget the soon-to-be onslaught of Euro-crazed demands for residential 3-phase receptacles and appliances! NEMA anticipated this long ago with L21-20 and L21-30 wiring devices. Be sure and stock up on ‘em on your next trip to the supply house.

Page 2 of 3 1 2 3