ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Recent Posts
VFD MotorFeeders
by gfretwell. 10/19/17 01:02 AM
Generator Cable Sizing
by brsele. 10/18/17 07:39 PM
What do you do?
by gfretwell. 10/17/17 01:08 AM
Good ol' copper pipe in the fuse holder trick
by HotLine1. 10/16/17 07:16 PM
Another generator question
by HotLine1. 10/16/17 07:02 PM
New in the Gallery:
Gallery Test
Popular Topics(Views)
241,388 Are you busy
177,345 Re: Forum
168,958 Need opinion
Who's Online Now
0 registered members (), 37 guests, and 7 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#98049 - 05/01/06 01:01 PM Motors  
kyelectric  Offline
Member
Joined: Aug 2005
Posts: 64
When installing a motor...Shouldn't you rate the fuses at 125% of FLA and the overloads should be set to run at FLA? Thanks


2017 / 2014 NEC & Related Books and Study Guides

#98050 - 05/01/06 02:20 PM Re: Motors  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,123
Estero,Fl,usa
Fuses have to handle LRA for a significant part of a second and higher than FLA for another second or so depending on load.
430.52 says you can use 300% of FLA for a single element fuse and 175% of FLA for a time delay fuse.


Greg Fretwell

#98051 - 05/01/06 05:14 PM Re: Motors  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
OL heater selection depends on Service Factor. See 430.32(A)(1)

[This message has been edited by Redsy (edited 05-01-2006).]


#98052 - 05/02/06 05:27 AM Re: Motors  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
I agree with the other responses and will add that the OLs are based directly off the motors name plate rating.

The conductors, fuses or breakers are based on the HP and the info in Article 430 tables.

The conductors must be at least 125% of the table values

I do not recall an NEC minimum size for the fuses or breakers but common sense would say at least 125% and perhaps much higher for hard starting loads.


Bob Badger
Construction & Maintenance Electrician
Massachusetts


Member Spotlight
noderaser
noderaser
Portland, Oregon, United States
Posts: 404
Joined: March 2007
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.013s Queries: 14 (0.002s) Memory: 0.7598 MB (Peak: 0.8912 MB) Zlib enabled. Server Time: 2017-10-19 08:55:41 UTC