ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Advertisement:-Left

Custom and Personalized Fall Gifts and Decor
Halloween Gifts and Decor

Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 1,688 guests, and 5 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#97879 04/11/06 01:38 PM
Joined: Sep 2005
Posts: 99
T
Tripp Offline OP
Member
Does URD (aluminum direct burial cable) go by a different name in the NEC? I'm looking for it in 310.16 and in ch.9 Tables 5 and 8 to calculate the proper size to use.

Work Gear for Electricians and the Trades

Workgear for Electricians

#97880 04/11/06 02:55 PM
Joined: Feb 2006
Posts: 25
F
Member
Here at the plant, URD is underground residential distribution cable. Typically, MV rated 15kv and up sold to POCO. Do you mean USE underground service entrance cable? Then table B.310.9 plays, I hope I haven't confused the issue. Chuck

#97881 04/11/06 05:48 PM
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
URD is not one of the conductor constuctions that is recognized by the NEC. Unless it has some other marking such as "XHHW" "RHW" then it would be a code violation to use it anywhere the NEC applies. See 310.13

Typically, the URD that I've run across is purchased because it is much less expensive than one of the correct cables or conductors. I've had to give the sad news to a lot of mobile home owners about this cable. Word has finally gotten around & the hardware stores are no longer selling it and it has been some time since I've seen a new piece of URD.


Few things are harder to put up with than the annoyance of a good example.
#97882 04/11/06 10:46 PM
Joined: Sep 2005
Posts: 99
T
Tripp Offline OP
Member
Well, this is confusing. I've worked in this locale for 7 years and everyone I know refers to this as URD. I shop at an electrical distibutor(wholesale house), not at a BigBox store or ma-n-pa hardware store, and they sell it as "URD". This is direct burial cable consisting of three aluminum conductors entwined with each other (I think one of the conductors has a reddish stripe, perhaps to distinguish it as the neutral). I've always wondered exactly what USE looked like, so maybe this is it. I guess I'll just stop by the wholesale house tomorrow and look closely at the wire itself to see exactly how it is labeled.
In the meantime, anyone else have an opinion?

#97883 04/11/06 10:56 PM
Joined: Sep 2005
Posts: 99
T
Tripp Offline OP
Member
Feather: I'm further confused by your mention of "table B.310.9." In this in the NEC? Not in my book. Just wondering.

#97884 04/12/06 04:57 AM
Joined: Jan 2003
Posts: 4,391
I
Moderator
B.310.9 is in Annex B at the rear of the code book.

Those tables are not for general use, they are for use by engineers.

Quote
B.310.15(B)(1) Formula Application Information.
This annex provides application information for ampacities calculated under engineering supervision.

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#97885 04/12/06 11:18 AM
Joined: Jul 2005
Posts: 46
R
Member
I believe that at least some of the cable that we call "URD" is in actuality a cable comprised of USE-2 conductors.

Here is a link to a cable company site for USE-2 cable

Chris

Work Gear for Electricians and the Trades

Workgear for Electricians

#97886 04/12/06 02:03 PM
Joined: Sep 2005
Posts: 99
T
Tripp Offline OP
Member
Went to the wholesale house today and found that what we all here refer to as URD is in fact labeled USE-2,RHH,RHW-2.

Apologies to Feather: Table B.310.9 is indeed in my codebook (thanks, Bob, for reminding of the annex I never visit).


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5