ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
Linear Power Supply Quits Under Load
by sabrown. 10/17/18 05:06 PM
220/230/240V 60Hz Systems
by dsk. 10/17/18 01:25 PM
PLC/HMI Enclosure C2, D1
by ghost307. 10/16/18 03:31 PM
Tingle off the water spigot
by dsk. 10/15/18 02:36 PM
New in the Gallery:
What is this for?
Plug terminals
Who's Online Now
0 registered members (), 30 guests, and 10 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Fire Alarm Wiring #97806
03/28/06 05:46 PM
03/28/06 05:46 PM
G
George Little  Offline OP
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Based on the 2002 NFPA72, is it now permissible to have the outgoing and return conductors in the same bridle rings when installing a Class A fire alarm circuit??

[This message has been edited by George Little (edited 03-28-2006).]


George Little
2017 / 2014 NEC & Related Books and Study Guides
Re: Fire Alarm Wiring #97807
03/28/06 06:31 PM
03/28/06 06:31 PM
R
Ron  Offline
Member
Joined: Mar 2002
Posts: 582
White Plains, NY
Generally yes, same bridle ring, different cable, unless specified by Contract differently.

6.4.2.2.2 All styles of Class A circuits using physical conductors (e.g., metallic, optical fiber) shall be installed such that the outgoing and return conductors, exiting from and returning to the control unit, respectively, are routed separately. The outgoing and return (redundant) circuit conductors shall not be run in the same cable assembly (i.e., multi-conductor cable), enclosure, or raceway.

Exception: The outgoing and return (redundant) circuit conductors shall be permitted to be run in the same cable assembly, enclosure, or raceway under any of the following conditions:
(1) For a distance not to exceed 3 m (10 ft) where the outgoing and return conductors enter or exit the initiating device, notification appliance, or control unit enclosures.
(2) Single conduit/raceway drops to individual devices or appliances.
(3) Single conduit/raceway drops to multiple devices or appliances installed within a single room not exceeding 92.9 m2 (1000 ft2) in area.

[This message has been edited by Ron (edited 03-28-2006).]

[This message has been edited by Ron (edited 03-28-2006).]


Ron
Re: Fire Alarm Wiring #97808
03/28/06 11:26 PM
03/28/06 11:26 PM
G
George Little  Offline OP
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
What happened to the required spacing (recommended) called out in the appendix?


George Little
Re: Fire Alarm Wiring #97809
03/31/06 12:02 AM
03/31/06 12:02 AM
R
Ron  Offline
Member
Joined: Mar 2002
Posts: 582
White Plains, NY
The annex text is still there, but Annex A is not a part of the requirements of the NFPA document but is included for informational purposes only.

A.6.4.2.2.2
A goal of 6.4.2.2.2 is to provide adequate separation between the outgoing and return cables. This separation is required to help ensure protection of the cables from physical damage. The recommended minimum separation to prevent physical damage is 305 mm (1 ft) where the cable is installed vertically and 1.22 m (4 ft) where the cable is installed horizontally.



[This message has been edited by Ron (edited 03-30-2006).]


Ron

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Samurai
Samurai
Fl.
Posts: 46
Joined: May 2007
Show All Member Profiles 
Top Posters(30 Days)
sparky 11
Popular Topics(Views)
250,397 Are you busy
188,007 Re: Forum
177,574 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.022s Queries: 14 (0.004s) Memory: 0.9603 MB (Peak: 1.0914 MB) Zlib enabled. Server Time: 2018-10-18 22:26:40 UTC